I found both legs on my split phase for both my air conditioners were crossed. The diagram below shows what I mean:
So for the 16 years my house has been built, one 120 volt leg of the split phase leg from each air conditioner goes into Air Conditioning Circuit Breaker 1; the other leg of the split phase from each air conditioner leg goes into Air Conditioning Circuit Breaker 2.
I was testing circuits for my back up battery for my upcoming solar installation and I was puzzled when I tripped one circuit breaker, and both shut down. After a bit of trouble shooting I found the "wires were crossed." The four ton unit has a 40 amp circuit breaker and the five ton unit has a 50 amp circuit breaker, so you can see how I'm not happy about one leg of a 50 amp circuit going through a 40 amp breaker.
I will be getting someone out to fix this wiring. I hope it is as simple as changing where two wires terminate in a circuit breaker.
So for the 16 years my house has been built, one 120 volt leg of the split phase leg from each air conditioner goes into Air Conditioning Circuit Breaker 1; the other leg of the split phase from each air conditioner leg goes into Air Conditioning Circuit Breaker 2.
I was testing circuits for my back up battery for my upcoming solar installation and I was puzzled when I tripped one circuit breaker, and both shut down. After a bit of trouble shooting I found the "wires were crossed." The four ton unit has a 40 amp circuit breaker and the five ton unit has a 50 amp circuit breaker, so you can see how I'm not happy about one leg of a 50 amp circuit going through a 40 amp breaker.
I will be getting someone out to fix this wiring. I hope it is as simple as changing where two wires terminate in a circuit breaker.