Background:
This is my first post to this forum. I have been designing a dual Sol-Ark 15K system for my new property since last fall and I am working through the last few details that are bugging me. I am located in Ohio under NEC 2017 and plan to be grid-tied with net metering to start, eventually headed to an off-grid setup in several years (hence the dual 15Ks). The AHJ said I can DIY solar as long as I have stamped electrical plans (still in work, my first draft is done, need to do a second pass).
Question 1:
AC and DC in the same wireway. I see it all the time on YouTube and this forum where people install a wireway under their Sol-Arks. Referring to the NEC 2017 code, this section bugs me when it comes do doing a wireway with PV, battery, and AC circuits all in the same wireway. My interpretation is in the code below so you can see why I am stuck on this.
NEC 2017 - 690.31 (B)
(B) Identification and Grouping. PV source circuits and PV output circuits (wires from my panels?) shall not be contained in the same raceway, cable tray, cable, outlet box, junction box, or similar fitting as conductors, feeders, branch circuits of other non-PV systems (the grid input? a generator input?), or inverter output circuits (Sol-Ark Load?), unless the conductors of the different systems are separated by a partition.
Has anyone under NEC 2017 had an inspection done and had success or problems with this? I would hate to install a wireway and find out I had to change it. I have emailed the AHJ on this, but haven't received a response. Also emailed someone who does Sol-Ark installs and haven't received a response.
Background for Question 2:
I will only be installing 1 of the 2 Sol-Ark 15s in Phase 1 of my project. The 2nd will come when I have made the final decision to go off-grid. Thus, I will be wiring my 200A utility service into a single Sol-Ark, and feeding my 200A breaker panel out of the single Sol-Ark in Phase 1 (in general terms). So I will need 4/0 AL wire, which will either be SER cable or individual 4/0 wires to handle 200A.
Question 2:
The Sol-Ark 15K has 1.5" trade size knockouts. Assuming THHN or THWN-2 wire, this only handles 2 wires (EMT) or 1 wire (FMC) at 4/0. I could go to copper 200A conductors at 2/0, but then I am at 3 wires (EMT or FMC) and that still leaves me hanging if I need to bring in 2 hots, a neutral, and a ground. If I bring in an 4/0 SER cable, I need a 2" knockout for the connector. 2" knockouts would be better since that size allows four 4/0 conductors.
How do other people meet conduit fill code with the 1.5" knockouts? I would like to just enlarge the LOAD and GRID knockout holes to 2" or make new ones if there is room. I have a hydraulic punch I could use to do this. Need to ask Sol-Ark if this voids the warranty.
Tangent: Looking at FMC conduit if a wireway doesn't work out and also because I can't find a cheap conduit bender for 1.5 - 2" EMT. I might try something with lots of LBs so I can use EMT or IMC without needing to bend it.
Summary:
As you can tell, I want to make sure I can answer every part of the code when I get inspected because I don't want any expensive re-work. I am replacing my electrical panel soon as part of this project and hope to ask my AHJ some questions and get a feel for their strictness during that inspection, but I would appreciate any advice on these two items.
This is my first post to this forum. I have been designing a dual Sol-Ark 15K system for my new property since last fall and I am working through the last few details that are bugging me. I am located in Ohio under NEC 2017 and plan to be grid-tied with net metering to start, eventually headed to an off-grid setup in several years (hence the dual 15Ks). The AHJ said I can DIY solar as long as I have stamped electrical plans (still in work, my first draft is done, need to do a second pass).
Question 1:
AC and DC in the same wireway. I see it all the time on YouTube and this forum where people install a wireway under their Sol-Arks. Referring to the NEC 2017 code, this section bugs me when it comes do doing a wireway with PV, battery, and AC circuits all in the same wireway. My interpretation is in the code below so you can see why I am stuck on this.
NEC 2017 - 690.31 (B)
(B) Identification and Grouping. PV source circuits and PV output circuits (wires from my panels?) shall not be contained in the same raceway, cable tray, cable, outlet box, junction box, or similar fitting as conductors, feeders, branch circuits of other non-PV systems (the grid input? a generator input?), or inverter output circuits (Sol-Ark Load?), unless the conductors of the different systems are separated by a partition.
Has anyone under NEC 2017 had an inspection done and had success or problems with this? I would hate to install a wireway and find out I had to change it. I have emailed the AHJ on this, but haven't received a response. Also emailed someone who does Sol-Ark installs and haven't received a response.
Background for Question 2:
I will only be installing 1 of the 2 Sol-Ark 15s in Phase 1 of my project. The 2nd will come when I have made the final decision to go off-grid. Thus, I will be wiring my 200A utility service into a single Sol-Ark, and feeding my 200A breaker panel out of the single Sol-Ark in Phase 1 (in general terms). So I will need 4/0 AL wire, which will either be SER cable or individual 4/0 wires to handle 200A.
Question 2:
The Sol-Ark 15K has 1.5" trade size knockouts. Assuming THHN or THWN-2 wire, this only handles 2 wires (EMT) or 1 wire (FMC) at 4/0. I could go to copper 200A conductors at 2/0, but then I am at 3 wires (EMT or FMC) and that still leaves me hanging if I need to bring in 2 hots, a neutral, and a ground. If I bring in an 4/0 SER cable, I need a 2" knockout for the connector. 2" knockouts would be better since that size allows four 4/0 conductors.
How do other people meet conduit fill code with the 1.5" knockouts? I would like to just enlarge the LOAD and GRID knockout holes to 2" or make new ones if there is room. I have a hydraulic punch I could use to do this. Need to ask Sol-Ark if this voids the warranty.
Tangent: Looking at FMC conduit if a wireway doesn't work out and also because I can't find a cheap conduit bender for 1.5 - 2" EMT. I might try something with lots of LBs so I can use EMT or IMC without needing to bend it.
Summary:
As you can tell, I want to make sure I can answer every part of the code when I get inspected because I don't want any expensive re-work. I am replacing my electrical panel soon as part of this project and hope to ask my AHJ some questions and get a feel for their strictness during that inspection, but I would appreciate any advice on these two items.