Thanks for the clarification.Note NEC 220.5(B):
Calculations shall be permitted to be rounded to the nearest whole ampere, with decimal fractions smaller than 0.5 dropped.
PV Current calculations, per NEC 2020 690.8(B), largest of 2 methods:
690.8(A) Current 9.63 Isc amps * 2 in parallel * 1.25 = 24.075 amps
1. Without Adjustment and Correction Factors:
24.075 amps * 1.25 = 30.09375 amps or 30 amps2. With Adjustment and Correction Factors:
24.075 amps / 0.88 temp correction @ 40c for 75c conductor / 0.80 adjustment for 4 conductors in conduit = 34 amps24.075 amps / 0.91 temp correction @ 40c for 90c conductor / 0.80 adjustment for 4 conductors in conduit = 33 amps.temp corrected for outside part of runs worst case.
Both within the ampacity of 10 AWG using a 75c or 90c conductor.
Which of those is ampacity needs to be under the 30A overcurrent protection limit and which of those are allowed to go over it?