I would like to know those while charging at 25 to 30 amps?
I did recharge again today.
Please note we have 2 types of electricity power here... Private generator for the city, and main grid from the government.
When main grid cuts, generator gives power to the city and vise versa.
.......................................
Setup = Bulk 61v / float 57.6v / charge 30amps
Results are .
Charging Starting from 47v.
Grid voltage 225v (private generator power):
From 47v to 55.8v @27amps = 1 hour.
Grid voltage became 240v (government main power):
From 55.8v to 56.4v @25amps = 20 minutes
From 56.4v to 57.2v @24amps trickling down to @7amps = 2 hours
Government Power went off, generator power came (230v):
From 57.2v to 57.4v @8amps trickling down to @3amps = 1:40 hours
From 57.4v to 57.5v @1amp = 30 minutes
From 57.5v to 57.6v @*zero amps * (inverter shows zero amps charging) = 1:45 hours.
Charging stopped at 57.6v (charging light not blinking anymore)
...................................................
Note: Charging never reached 61v as per bulk setup (61v).
During the charging process, i decreased the float to 54.4v and the charging voltage started to go down very fast to follow the float setup and not the bulk setup. (I increased it again to 57.6v to keep the charge going).
Voltage of inveter screen and inverter pins where the same, batteries were lower by 0.01v (from 47v till 57v)
Eg: inverter 56.1 / pins 56.1 / batteries 56
From 57v till 57.6v all 3 readings were exactly the same.
PS: from 57 to 57.6 I could hear the batteries Boiling.
This procedure took 8 hours, while replying to you here I decreased the float from 57.6v to 54.4v after those 8 hours, inverter went down very fast to 54.4v