Looking over the threads to find info on spikes related to inrush I found you here, so you'd probably be the best fellow here to ask. I checked the inrush and running amp of my compressor as the kpv is not starting it at this point. On the meter it shows 32amp on 1 leg and close to 40 amp on the other for about a second. After start up shows 16.5 A -leg 1 and 20 A - leg2 running amps. SS offers several soft starts. After looking them over if you have a chance, could you recommend 1 of them for this? I checked this close to the compressor for these reading. At the farthest point of the run closest to the inverter, the readings of inrush seem to be much less. These reading were done with utility grid. Reading on motor: Baldor Cat.No. 2023000868 / HP5 / V 230 / AMPS 22 / Frame 184T / HZ 60 /PH 1 / SER.F. 1,15 / code j / DES. L / CLASS F /NEMA NOM. EFF. 82.5% / P.F. 89%