I have those but not by choice. They are inexpensive. I’ve had bad ones, but that’s not too common. Have you actually measured it with a clamp meter or looked at what the inverter says?siemens
I have those but not by choice. They are inexpensive. I’ve had bad ones, but that’s not too common. Have you actually measured it with a clamp meter or looked at what the inverter says?siemens
For US domestic breakers you’re 100% correct.I don't go and try and correct Hedges lightly, but no. Breakers are rated to trip at their rated current, not 80%. The trip curve in the data sheet for any AC breaker will show this.
The NEC says that you should not size permanently installed equipment to draw more than 80%, but that's a different issue.
they are both 240vAre they 115 or 230v mini splits?
If they're both 115 one probably needs to be moved to the other leg.
Ok, then I am confused how much power they demand.they are both 240v
I dont know if my emporia vue is giving me bad info or what.Ok, then I am confused how much power they demand.
24A 240V is a LOT of draw from a single minisplit...
Can you post the service tag from the h?
yes, change it for a new 60a breakerWhen you say change 60a breaker, you mean like for like replacement and not going up in size?
solar assistant showed about 6000w loadWhat does your AIO's show in the way of AC out wattage? They should have a readout.
OK maybe this is also what Im confused about6000w/240vAC=25a
ETA: If you are running 2-6500w units as split phase you are just about maxed.
Sorry my error. I made the mistake of thinking each AIO was seeing 6000w. Instead they are seeing only half each. Each leg of your 240vAC would indicate 12.5a. if you tossed a clamp on meter on either L1 or L2.OK maybe this is also what Im confused about
solar assistant and emporia both showed using 6000w
lets say all of the load is 240v
each of the minisplits are only using 15a, running 240v, thats 15a on L1 from 1 inverter and 15a on L2 from the other inverter
So running 2 minisplits at 15a each, I have 30a on L1 from one inverter and 30a from the other inverter
I thought the inverters can output about 54a each at 120v
what dont I understand about split phase so the system is maxing out at 25a ?
ok thanksSorry my error. I made the mistake of thinking each AIO was seeing 6000w. Instead they are seeing only half each. Each leg of your 240vAC would indicate 12.5a. if you tossed a clamp on meter on either L1 or L2.
At any rate the problem seems to be your breaker and not your load.
Its my understanding thats off both legs. so 25A L1-N and 25A L2-N I am fairly certain you can not pull 50A off L1-N (0A L2-N)the 6548 inverters run 120v each so 6500/120 is about 54 amps max output for each inverter
Amps in a 230V system do not add up.Its my understanding thats off both legs. so 25A L1-N and 25A L2-N I am fairly certain you can not pull 50A off L1-N (0A L2-N)
it matters when you start stacking 110v loads on a 220v split phase system.
I understand that. however the quote that i copied from OP's post suggested 54a of 120v. I was clarifying that you cant pull 54a off one leg.Amps in a 230V system do not add up.
If you have 240V on l1 to l2, you measure 25A on either l1 or l2, you have 25A...
Not 50...
I was thinking that the LV6548 was a native 220v inverter. IT is not. As a single unit it ONLY supports single phase. so yes you can pull 54a off one L-N connection.is there a max imbalance between L1 and L2 that would cause either the inverter to shut down or the main breaker to trip, when total usage is below max on both legs ? in other words a breaker trip or inverter shut down just due to imbalance rather than overload ?
this would be in a dual inverter split phase setup like mine
I may need to verify how off balance I might be and move breaker positions