Wiring spd in combiner box

cho

New Member
Joined
Oct 21, 2021
Messages
25
I notice that in some combiner boxs surge protection device is wired positive to negative and negative to positive. Why?
combox.jpg
What is correct positive to positive or positive to negative? And is that important?
 
Consider the PV the current source not the inverter. Yes polarity is important because SPD's may arc over and not offer protection.
 

Attachments

  • Discussion-Paper-Correct-Wiring-of-Double-Pole-DC-Breakers-LVL2-131210-v2.pdf
    1.7 MB · Views: 67
Thank you Mopat for correct wiring DC breakers document.
That was new informations for me.

But I still don't understand how to properly connect SPD in combiner box.
Does I need to connect positive (+) to negative (-) / negative (-) to positive (+)
or positive (+) to positive (+) and negative (-) to negative (-)

spd2.jpg
in this diagram SPD is wired negative to positive / positive to negative
 
Last edited:
positive (+) to positive (+) and negative (-) to negative (-)

PV positive to SPD/(breaker) positive, negative to negative.

Attached may further clarify.
 

Attachments

  • DC breaker wiring.jpg
    DC breaker wiring.jpg
    144.9 KB · Views: 81
pole.jpg

On this picture what does it mean "only in theoretical example"
Is that mean that one pole circuit breaker goes only on positive wire or can be put also on negative wire?
Like you can see in my combiner box circuit breaker is on negative wire. Is that correct?
 
Thank you Mopat for correct wiring DC breakers document.
That was new informations for me.

But I still don't understand how to properly connect SPD in combiner box.
Does I need to connect positive (+) to negative (-) / negative (-) to positive (+)
or positive (+) to positive (+) and negative (-) to negative (-)

View attachment 72720
in this diagram SPD is wired negative to positive / positive to negative
?????

Isn't this wiring wrong?

I mean after a surge, there is a chance that the SPD will blow the fuse but not tripping the left-most MCB, the load is no longer protected by the SPD.
 