House burned down

Be really careful testing those fuses.

Stored energy is dangerous.

After OP showed those pictures am sure fuse and breaker sales skyrocketed. Hopefully this will somehow help other ppl from having a problem.


IMG_6296.jpeg
IMG_6293.jpeg

IMG_6297.png
 
  • Unsure
Reactions: D71
What is going on with that DC disconnect wiring? Three positives going in and three positives out?
Not sure what was changed but think op changed batteries….after these were put up. Link at bottom.

IMG_6446.png

IMG_6444.png

IMG_6443.jpeg


The wire way melted away.
 
I think insurance still pays. There are too many rural counties with No inspection for anything. And you can still get insurance

The the subdivision down near Cortez me and the wife are moving to requires an electrical permit be pulled when being built, but no inspections after that. The PoCo will only inspect if you grid tie and sell back.
 
Not sure what was changed but think op changed batteries….after these were put up. Link at bottom.

View attachment 215219

View attachment 215220

View attachment 215221


The wire way melted away.

The op changed shelves and Added a 7th string after. The black cabinet is gone. There are pictures in the powerwall thread by the OP.
 
  • Like
Reactions: D71
The the subdivision down near Cortez me and the wife are moving to requires an electrical permit be pulled when being built, but no inspections after that. The PoCo will only inspect if you grid tie and sell back.
Had a friend ask to use my electrical license in a rural Ohio county. He said Duke utility didn’t require a permit just needed install by a licensed electrician. So I went to friends, checked his work, put some detox on fittings. And the Utility hooked him up.
 
So, after 4 to 5 years of working flawless, the 100 kwh lifepo4 battery caught fire at night and burned our house down. Luckily our family just made in out on time.
Inspection of the fire expert revealed that a melt fuse melted, and created an arc between the 2 points wich ultimatly started the fire.
So i learned to not use melt fuse anymore, plus once the house is rebuild, i will put the new system in a seperate shed outdoor.

Thought I'd share this. It was a set of AC 600 volt fuses on a 500 volt DC feed from the panels on a nice sunny day. If this were properly rated fuses, I wouldn't have taken this picture.

The current from the panels exceeded expectations and one of the fuses blew, effectively creating a 10KW arc lamp on my wall. This is why I have a renewed respect for electrical codes.
 

Attachments

  • Imagepipe_86.jpg
    Imagepipe_86.jpg
    144.2 KB · Views: 65
Fuses or breakers between panels and inverter create more fire hazard than safety benefits.
I think you have to use a fuse if paralleling more than two strings - I don’t have parallel strings; mine are all in series as I wanted high voltage. We did put in 600v DC Midnite SPDs between the panels and inverters. I don’t remember what the connectors that we used are called. They were like an industrial wego but the wires were secured with screws (I think). I’ll ask my electrician next time I see him.
 
I think you have to use a fuse if paralleling more than two strings
Even that is bogus reason if you really model most probable panel short circuit failure. Once you go above 2 panels in series per string you can have 1 bypass diode fail short and not cause excessive sink current across remaining cells. You would need 0.7V per cell to make it absorb 10A. If you got a bunch of panels in parallel (none in series) then fuses on each panel make sense.
 
Thought I'd share this. It was a set of AC 600 volt fuses on a 500 volt DC feed from the panels on a nice sunny day. If this were properly rated fuses, I wouldn't have taken this picture.

The current from the panels exceeded expectations and one of the fuses blew, effectively creating a 10KW arc lamp on my wall. This is why I have a renewed respect for electrical codes.
I'm guessing that was a steel enclosure and not the random Amazon plastic combiner boxes.
 
Would you just do something like an imo disconnect between them?
Sure something like PV isolator switch. But if you insist on using fuses/breakers then at least install them inside steel enclosure. Same for PV surge protectors. Another interesting point is that fuses are ineffective until 2x rated current. So for 10A panels you'd use 15A fuse that will not blow in reasonable time until 30A fault. That means 4 parallel strings are needed (1 faults and 3x10A supply current).
KLKD_fuse_time-current_chart.PNG
 
Last edited:
Thought I'd share this. It was a set of AC 600 volt fuses on a 500 volt DC feed from the panels on a nice sunny day. If this were properly rated fuses, I wouldn't have taken this picture.

The current from the panels exceeded expectations and one of the fuses blew, effectively creating a 10KW arc lamp on my wall. This is why I have a renewed respect for electrical codes.


What sort of fuse was it? I ask because a 600v fuse on a 500v feed shouldn't matter at all. With fuses it is all about the current running through it. Most fuses are way over the voltage used. The voltage limitation is all about the insulation.
 
Sure something like PV isolator switch. But if you insist on using fuses/breakers then at least install them inside steel enclosure. Same for PV surge protectors. Another interesting point is that fuses are ineffective until 2x rated current. So for 10A panels you'd use 15A fuse that will not blow in reasonable time frame until 30A fault. That means 4 parallel strings are needed (1 faults and 3x10A supply current).
View attachment 215314
Yes, metal enclosures for sure. I'm switching my mnpv6 combiner box over to fuses from 150V mnepv breakers now that I have the 450/100. Also a good place to transition from PV cable to fine stranded to go to the sccs.

20240514_101637.jpg
 
No! The limitation is often the ability to break DC voltage (DC rated AIC).


The DC voltage rating isn't the AIC rating - they are different all together. The voltage rating is where it won't arc over/through the insulation into anything else. The AIC rating is the ability to break an arc inside when it opens. The AIC is always rated in amps or kilo-amps, not volts
 
Last edited:
AIC rating can vary with voltage.

Interrupt Capacity
information.png
10000A @ 14V DC
5000A @ 32V DC
2000A @ 58V DC

 