If that breaker was used with the "+" terminal connected to battery positive, and "-" terminal connected to battery negative, with load connected to the unlabeled terminals, it could interrupt current to shut off the load. In the event of a short circuit, it should do so for a battery able to deliver up to 10,000A, but wouldn't be suitable for one able to source more current (into a short.)
If used between battery and SCC, the issue is that massive current flows one direction if there is a short at the SCC, and moderate current flows from SCC to battery. There are some recommendations of which way to orient it, choosing the lesser of two evils.
If used for one PV string (or one PV array), it could have "+" terminal connected to PV positive lead, "-" to PV negative lead, other side goes to SCC. It shows ratings for up to 250Voc, and being a thermal-magnetic breaker, would be suitable for 50A continuous, 80% of its rating. Because PV panels can deliver an estimated 25% over Isc under some illumination conditions, good for up to 40A Isc array.
What I don't think it is good for is 3 or more PV strings (or arrays) each with this breaker, and connected in parallel. If one string shorts, the others could dump current through its breaker in reverse direction, and a polarized DC breaker can't interrupt that.
You can get some DC breakers that are non-polarized. Those are better if paralleling 3 or more PV strings, or for bidirectional applications like SCC to battery.
If used between battery and SCC, the issue is that massive current flows one direction if there is a short at the SCC, and moderate current flows from SCC to battery. There are some recommendations of which way to orient it, choosing the lesser of two evils.
If used for one PV string (or one PV array), it could have "+" terminal connected to PV positive lead, "-" to PV negative lead, other side goes to SCC. It shows ratings for up to 250Voc, and being a thermal-magnetic breaker, would be suitable for 50A continuous, 80% of its rating. Because PV panels can deliver an estimated 25% over Isc under some illumination conditions, good for up to 40A Isc array.
What I don't think it is good for is 3 or more PV strings (or arrays) each with this breaker, and connected in parallel. If one string shorts, the others could dump current through its breaker in reverse direction, and a polarized DC breaker can't interrupt that.
You can get some DC breakers that are non-polarized. Those are better if paralleling 3 or more PV strings, or for bidirectional applications like SCC to battery.