I’d still love to see a 10% SOC 280ah battery connected in parallel with a say 90% SOC 280ah and watch the in rush current, can’t imagine it’d cross 200a.
I'll add it to the todo list for once I have the cells to build my next two packs.
I’d still love to see a 10% SOC 280ah battery connected in parallel with a say 90% SOC 280ah and watch the in rush current, can’t imagine it’d cross 200a.
Braver man than I!I'll add it to the todo list for once I have the cells to build my next two packs.
The 5-wire "main cord" is shown as a switched grounding connection in Nami's previous diagrams.Is there a wiring diagram for that handy? I was planning on using that feature but didn't know I'd need additional hardware to do so.
Braver man than I!
Andy at Offgrid garage did just that only he used closer to 0% (2.5v) vs 100% (3.65v) You can watch it go crazy high amps (or not) starting at 12:30Looks like JK 200a 4s-8s is now parallel compatible, just depends on system design and the need of class T for each battery bank before bus bar, you know a properly designed system. Screen shot taken from hankzor listing.
I’d still love to see a 10% SOC 280ah battery connected in parallel with a say 90% SOC 280ah and watch the in rush current, can’t imagine it’d cross 200a.
Andy’s test was 100% charged and 0% charged and def shows that current would exceed the current limit but that’s an extreme test, there has to be a mid point where damage won’t happen.
He did is slowly so that he could monitor and make adjustments rather than an all or nothing. The point was that even at the extreme 0%/100% the current was not off the charts. Yes, it did exceed the 200A limit on his meter but not by much. This is evident by the fact that after a few seconds of messing with it, he was able to tighten everything down and it was less than 200. His point was that as long as you are not going to the extremes of differential voltage (outside of the knees) then you can connect and there will be only minor current (60A or so)So 0% and 100% is bad mojo, what about 10 and 90? Or 20 and 80?
I didn’t like how he slowly clamped the bus bars, sure it was his method of protection, but it glossed over true inrush current at the lower delta cells of say a BMS/breaker closing in. There’s bound to be a safe margin. He’s shown it multiple times on his three bank set up it, opening and closing breakers.
They have too much delay, in shutting down the sudden excessive current. The BMS (for either the sender or receiver) could be easily become fried, if this instantaneous amount exceeds the maximum instantaneous capability of the BMS. That would either leave the battery completely unprotected, or totally unusable.If cheap 150 or 200 amp anl fusses are used It shouldnt be too bad.
I agree that "slow clamping of the bus bars" provided a highly effective (and undesirable) additional protection. He should have had the bars clamped tight from the beginning, and used a 500A battery switch to engage the connection.So 0% and 100% is bad mojo, what about 10 and 90? Or 20 and 80?
I didn’t like how he slowly clamped the bus bars, sure it was his method of protection, but it glossed over true inrush current at the lower delta cells of say a BMS/breaker closing in. There’s bound to be a safe margin. He’s shown it multiple times on his three bank set up it, opening and closing breakers.
Thanks for clearing up the red and black wires on the heating port pigtail. Has anyone determined if the JK BMS records the current being drawn thru the heating port?And, was this "verbal diagram" sufficient for you?
No idea - yet. I'll report if I see such a number in either the hard-wired monitor or the Android App. In any case, I'll be using a pretty accurate "coulomb counter" monitor on that interface during upcoming testing, and I can compare any JK- presented number (on the hard-wired monitor, of the Android App) to the current being shown on the "coulomb counter".Thanks for clearing up the red and black wires on the heating port pigtail. Has anyone determined if the JK BMS records the current being drawn thru the heating port?
Andy (Off Grid Garage) ran into that same error. It is due to the default config being set to 8 cells rather than 4 in your setup. You might rewatch his review as he ran across a couple of other little gotchas on the road to getting it workingAn "ERR" code within a box in the upper left side of the display, showing code 9.
- A small red warning triangle on the upper right side.
- The very curious value 0.0%, in big yellow lettering, is present in the middle of the Display (presumably referring to a calculated remaining SOC).
- Below that 0.0% value, a bright bar indicates the battery to be almost completely full, and the correct voltage 13.2V is shown on the lower right.
Another of the things that Andy found was that the default chemistry was not LFP so that needed to be changed as well as the limits.Andy (Off Grid Garage) ran into that same error. It is due to the default config being set to 8 cells rather than 4 in your setup. You might rewatch his review as he ran across a couple of other little gotchas on the road to getting it working
I can now connect, but cannot set parameters from the Bluetooth/Android App. It insists that I have "failed password verification" every time, both before resetting the default PW ('1234') and modifying it to be '12345'. Restarted the phone and the BMS as well, for both password values.Andy (Off Grid Garage) ran into that same error. It is due to the default config being set to 8 cells rather than 4 in your setup. You might rewatch his review as he ran across a couple of other little gotchas on the road to getting it working
Or 12345678I think it is 123456
The manual linked from within the Resources has that password in it: https://diysolarforum.com/resources/jk-bms-active-bluetooth-bms-manual.250/The '123456' default password to change settings is not yet documented in the draft manual's English translation. I'm in!