Will it work? Supplementing off grid inverter/battery with on grid PV inverter in one system.

Yes, as stated in my profile.
I believe you can achieve the same thing by shutting the grid tie inverter off using a relay or using the dry contacts on an off grid inverter. Won't be as elegant but it would work, imo
 
I believe you can achieve the same thing by shutting the grid tie inverter off using a relay or using the dry contacts on an off grid inverter. Won't be as elegant but it would work, imo
Countless ways to skin a cat if you use your head along the way.
 
The aro battery is 4 times as expensive as a regular battery. Not a great idea for most people
If I were starting from scratch today I would seriously consider the eg4 powerpro and eg4 inverters. But, it appears to me from the traffic on this forum and other places that the EG4 products are still needful of frequent human intervention to keep them running properly- for me the most important thing was seamless integration between inverter/battery/powermeter with an expectation that after system is setup as desired it would be hands off - the system I have has been so in all the configurations I’ve had it in since the beginning between expansions.
 
4) I’m using the Growatt ARO batteries- I intend to add non-Growatt batteries to the grid-tie inverter at some point in the next year or so to bring it up to at least 36. Intend to reverse engineer the battery comm’s enough to be able to unless someone else does it first - got lots of other hobbies though so it’s on back burner. Gonna build a test rig this fall with a spare inverter to start looking at it. Casually looked at the modbus traffic in spring and it’s too complex to figure out quickly.

@MajicDiver; Thanks for the additional info, very helpful. When and if you figure out a DIY alternative to the ARO batteries please let me know. Would like to do the same but don't have the necessary back gound on the comms side of this.
 
An off grid inverter without AC coupling capabilities can't do it.
Thanks, can you elaborate as to why? Is it because a standard battery inverter cannot phase shift to throttle the grid tie inverter (hence the use of a smart meter) or potential damage to the battery inverter or ???
 
Thanks, can you elaborate as to why? Is it because a standard battery inverter cannot phase shift to throttle the grid tie inverter (hence the use of a smart meter) or potential damage to the battery inverter or ???
Feels like you’re missing some terminology or theory of operation here.

Frequency shift OR cutting a relay are the main ways to throttle, with the latter potentially being risky due to the potential for stressing the inverter since it’s not tested for so much disconnect cycles.

Not sure what you mean by smart meter.

If the battery inverter is not able to throttle the GTI then the GTI (absent some kind of output limiter, I’m not sure where you would set up a limiter in this picture in a simple way) will keep pushing its nameplate AC power until its anti islanding triggers and it shuts off. There is no UL safety requirement that the GTI must not burn up a off grid inverter, just that it disconnects from grid island within X parameters.

That power has to go somewhere. If there is no well defined sink for the power, then the power is going to get dissipated in random places and that’s probably going to be a fire-adjacent situation
 
Ah I finally read Magic’s profile. That zero export positioning is a good idea, though it does presume a certain response latency on the grid tie inverter/ability for the grid forming inverter to absorb over production/overvoltage within that time.

I would be kind of scared of firmware updates changing behavior. Zero export to grid has much larger safety margin against bugs/behavior changes.

Even with a hybrid that has AC coupling as a supported feature, it’s not like anybody is auditing what layers of firmware and physical protections there are against getting it wrong.
 
I have an existing 5KW grid connected PV system on my home; Growatt MIN 5000TL-X, 240 split phase. I am considering adding a 6KW Growatt SPF offgrid inverter/battery to provide backup power during power outages. The on grid and off grid inverters would both back feed breakers in the same main distribution panel.

During a utility power outage the main panel would disconnect from the grid (utility), and the offgrid inverter would connect to the main panel to provide backup power.

The question is what will happen if I leave the on grid inverter connected when the off grid inverter is powering the distribution panel? When the off-grid inverter is providing power to the distribution panel will the on grid inverter come back online providing supplemental power to the distribution panel reducing the load on the off grid inverter or will one or the inverters go into a fault condition (or worse)?

Easy enough to try, but before possibly damaging one or more inverters would appreciate hearing from others....

(PS: The 6kw off grid inverter is sufficient to power loads on this distribution panel)
View attachment 166721
The easiest thing may be to DC couple your current array to an mppt charge controller during an outage
 
I don't know of any that can 100% guarantee absolute zero export.
I don’t think that is the requirement here. Those zero export systems have to average out close enough to zero to satisfy the POCO.

The zero export when hacked up to support this unholy grid forming approach primarily needs to react fast enough to not scorch anything with overvoltage, and secondarily needs to keep anti-islanding disconnections to a minimum (a function of overvoltage). The PWM controller can probably detect a load anomaly (impedance much higher than expected) within a few PWM cycles without even needing the zero export feedback.
 
I don’t think that is the requirement here. Those zero export systems have to average out close enough to zero to satisfy the POCO.
The POCO may be fine with an average zero export.
It definitely won't do any damage to the grid.
An off grid inverter being forced to receive power through its output is a different story.
 
The POCO may be fine with an average zero export.
It definitely won't do any damage to the grid.
An off grid inverter being forced to receive power through its output is a different story.
Right. I wouldn’t have tried it myself but MajicDiver in this thread has been using strategically placed zero export for a long time to block the GTI from pushing too much into a dumb grid forming inverter and his inverters are still alive.
 
Right. I wouldn’t have tried it myself but MajicDiver in this thread has been using strategically placed zero export for a long time to block the GTI from pushing too much into a dumb grid forming inverter and his inverters are still alive.
Maybe I misread it. But I thought that he was using two hybrid inverters. One grid-tied and the other off grid?
If both are capable of AC coupling, then there wouldn't be a problem.
 
Maybe I misread it. But I thought that he was using two hybrid inverters. One grid-tied and the other off grid?
If both are capable of AC coupling, then there wouldn't be a problem.
Good point, AC coupling is in the spec for that inverter. I don’t think his SLD matches how growatt wants them to be tied together (there’s some kind of custom Growatt combiner/transfer switch box), but probably the protective capabilities are a function of the grid forming transformer’s response to the GTI’s behavior, EG safely absorb excess and dampen the anti-islanding detection.

I did not check the model number and assumed they had used some semi random off grid inverter.
 