I believe you can achieve the same thing by shutting the grid tie inverter off using a relay or using the dry contacts on an off grid inverter. Won't be as elegant but it would work, imoYes, as stated in my profile.
I believe you can achieve the same thing by shutting the grid tie inverter off using a relay or using the dry contacts on an off grid inverter. Won't be as elegant but it would work, imoYes, as stated in my profile.
Countless ways to skin a cat if you use your head along the way.I believe you can achieve the same thing by shutting the grid tie inverter off using a relay or using the dry contacts on an off grid inverter. Won't be as elegant but it would work, imo
Lol. Are you angry about life?Countless ways to skin a cat if you use your head along the way.
If I were starting from scratch today I would seriously consider the eg4 powerpro and eg4 inverters. But, it appears to me from the traffic on this forum and other places that the EG4 products are still needful of frequent human intervention to keep them running properly- for me the most important thing was seamless integration between inverter/battery/powermeter with an expectation that after system is setup as desired it would be hands off - the system I have has been so in all the configurations I’ve had it in since the beginning between expansions.The aro battery is 4 times as expensive as a regular battery. Not a great idea for most people
4) I’m using the Growatt ARO batteries- I intend to add non-Growatt batteries to the grid-tie inverter at some point in the next year or so to bring it up to at least 36. Intend to reverse engineer the battery comm’s enough to be able to unless someone else does it first - got lots of other hobbies though so it’s on back burner. Gonna build a test rig this fall with a spare inverter to start looking at it. Casually looked at the modbus traffic in spring and it’s too complex to figure out quickly.
Can be throttled.There are many grid tied that can throttle though
Thanks, can you elaborate as to why? Is it because a standard battery inverter cannot phase shift to throttle the grid tie inverter (hence the use of a smart meter) or potential damage to the battery inverter or ???An off grid inverter without AC coupling capabilities can't do it.
No, many grid tie inverters can self throttle with a zero export optionCan be throttled.
Something external must throttle them.
An off grid inverter without AC coupling capabilities can't do it.
Feels like you’re missing some terminology or theory of operation here.Thanks, can you elaborate as to why? Is it because a standard battery inverter cannot phase shift to throttle the grid tie inverter (hence the use of a smart meter) or potential damage to the battery inverter or ???
The easiest thing may be to DC couple your current array to an mppt charge controller during an outageI have an existing 5KW grid connected PV system on my home; Growatt MIN 5000TL-X, 240 split phase. I am considering adding a 6KW Growatt SPF offgrid inverter/battery to provide backup power during power outages. The on grid and off grid inverters would both back feed breakers in the same main distribution panel.
During a utility power outage the main panel would disconnect from the grid (utility), and the offgrid inverter would connect to the main panel to provide backup power.
The question is what will happen if I leave the on grid inverter connected when the off grid inverter is powering the distribution panel? When the off-grid inverter is providing power to the distribution panel will the on grid inverter come back online providing supplemental power to the distribution panel reducing the load on the off grid inverter or will one or the inverters go into a fault condition (or worse)?
Easy enough to try, but before possibly damaging one or more inverters would appreciate hearing from others....
(PS: The 6kw off grid inverter is sufficient to power loads on this distribution panel)
View attachment 166721
CorrectIs it because a standard battery inverter cannot phase shift to throttle the grid tie inverter
I don't know of any that can 100% guarantee absolute zero export.(hence the use of a smart meter) or potential damage to the battery inverter or ???
See aboveNo, many grid tie inverters can self throttle with a zero export option
I agree. I have possession of the current firmware and do not forsee a need to ever upgrade, if i do I will test and either retune or revert if necessary.I would be kind of scared of firmware updates changing behavior.
I don’t think that is the requirement here. Those zero export systems have to average out close enough to zero to satisfy the POCO.I don't know of any that can 100% guarantee absolute zero export.
The POCO may be fine with an average zero export.I don’t think that is the requirement here. Those zero export systems have to average out close enough to zero to satisfy the POCO.
Right. I wouldn’t have tried it myself but MajicDiver in this thread has been using strategically placed zero export for a long time to block the GTI from pushing too much into a dumb grid forming inverter and his inverters are still alive.The POCO may be fine with an average zero export.
It definitely won't do any damage to the grid.
An off grid inverter being forced to receive power through its output is a different story.
Maybe I misread it. But I thought that he was using two hybrid inverters. One grid-tied and the other off grid?Right. I wouldn’t have tried it myself but MajicDiver in this thread has been using strategically placed zero export for a long time to block the GTI from pushing too much into a dumb grid forming inverter and his inverters are still alive.
Good point, AC coupling is in the spec for that inverter. I don’t think his SLD matches how growatt wants them to be tied together (there’s some kind of custom Growatt combiner/transfer switch box), but probably the protective capabilities are a function of the grid forming transformer’s response to the GTI’s behavior, EG safely absorb excess and dampen the anti-islanding detection.Maybe I misread it. But I thought that he was using two hybrid inverters. One grid-tied and the other off grid?
If both are capable of AC coupling, then there wouldn't be a problem.