You can't test it, in this configuration.
You can't test it, in this configuration.
No, you can't test it with grid connected.Oh, maybe I'm just misunderstanding things, so to test it I need to be running grid for passthrough?
No, you can't test it with grid connected.
Turn off the inverter.So how do I know the dynamic bonding is working (if I have it)
Make sure no wires are connected to AC IN and AC Out. With inverter off check continuity between G/N on AC out (should not be any). Turn inverter on and wait for the relay clicks on boot, if you have continuity between G/N on AC Out it's bonded.
I'd verify how each unit is configured indpendantly first. For split phase, I'd call the vendor or manufactuer for guidance. I recall a video from Will and a few others with these types of inverters that one unit had to retain a bond but I think that was for off-grid (never an AC IN) only.I will give that a try, what about when running two units in split phase
Make sure no wires are connected to AC IN and AC Out. With inverter off check continuity between G/N on AC out (should not be any). Turn inverter on and wait for the relay clicks on boot, if you have continuity between G/N on AC Out it's bonded.
It does have dynamic bonding.
Put the screws back in.
And hook everything back up.
Do not jumper the input neutral to the output neutral.
First half is incorrect.
Second half is correct.
Yes, as long as it's not using the grid.So I should have continuity all the time? Unit off and unit on?
Yes, as long as it's not using the grid.