Better way to arrange main fuses, DC disconnect, busbars etc?

cyberwombat

New Member
Joined
Aug 22, 2022
Messages
15
Location
Flagstaff, AZ
I am working on a parallel battery setup (so two wires going out) and a dual inverter setup. My diagram.... works but feels messy with all these 3 spot busbars I would need. Wondering if there is a better way to manage all this? Ive looked at the Lynx Distribution and Power In but I dont think that will really help much as I still have shunts/disconnects/main fuses to work with. Perhaps rearranging things but not sure. Open to suggestions. Image is preview - attached PDF is whole thang.

Screenshot 2024-03-13 at 12.25.51 PM.png
 

Attachments

  • 3 Line.pdf
    768.1 KB · Views: 2
Re look at Victron- The PowerIn (w/fuses added) and bolt the end sticking out to the shunt and to the on/off switch. YouTube “explorist life” shows it in their videos. That eliminates two large short cables.


Good Luck
 
Ive looked at this setup but it didnt seem to save much. Id be replacing the current 2 prong busbar to the DC disconnect with this. I suppose I could consolidate some of the neg busbar into it - the ground cables can prob go in one... Did find this which might be a solution though still got this dangling fuse/dc disconnect. I heard Midnite solar may have an all in one but havent found it yet.
 
Last edited:
I would put a breaker on the output of each 24 volt string. More like:

( battery A ) - ( battery B ) - -- (breaker ) ---- ( positive bus bar )

( battery C ) ---- ( battery D ) ---- ( breaker ) ---- ( positive bus bar )


( Inverter A ) ---- ( breaker ) ----- ( positive bus bar )

( solar ) ----- ( breaker ) ----- ( positive bus bar )

( fuse block ) - -- ( breaker ) - -- ( positive bus bar ) - for small loads like signals, etc.

______________

On the negative side, similar.

( battery A ) ----- ( etc ) ------ (battery negative bus bar ) --------- (shunt ) ---- ( system negative bus bar )

Same for the second battery string.

Then

(inverter 1 negative ) - (system negative bus bar )

etc.

Example breaker.

https://www.bluesea.com/products/category/14/30/Circuit_Breakers/187-Series

You will need some higher count bus bars to pull it all together. Might require connecting a few together.


______________

There will be times when you will want to isolate off various sections of it and this also makes system re-sets easy.
 
Last edited:
Thanks for all your suggestions. I've revised my plans to use a couple of Lynx Distributors in "reverse" mode as I have seen to manage multiple batteries/inverters. That allows me to have dedicated fuses for each battery string. Im not totally sure I wont need to add a copper bar to connect the two distributors unless the dc disconnect and the shunt are the same spacing but that should be easily workable.
Also now have dedicated ground bar and a single earth rod. I am bonding the PV frames and structure to the EMT conduit and then to the ground busbar. Seems having a single rod is the way to go else connect both rods by wire though am not sure which is best here or if it matters - the array is 100' from equipment. Appreciate any input.
Screenshot 2024-03-16 at 2.09.35 PM.png
 

Attachments

  • 3 Line Revised.pdf
    691.4 KB · Views: 2
I have but for the moment am trying to do bare min to get my plans approved. Will def expand later with one of those, split phase, generator etc but want to work with small bites (i.e. less $ too)
 