Generator Boost with newest Firmware
Is this basically just protecting the generator input port to only what it's capable of producing without overloading the generator? What happens if the loads try to pull more than the gen+solar/bat are capable of providing per the max generator boost config?Generator Boost with newest Firmware
Can someone help me understand why my new 18kpv would randomly switch off of battery to grid for a few minutes several times per day? For context I do not have solar installed yet and am just running off of battery in a grid tied scenario.
I asked Markus and he said it was from grid frequency going out of spec so he made some changes but it is still happening just as much. Has anyone seen this with their 18kpv? I can understand why it might switch from grid to battery if there’s an issue but why would it switch from battery to grid seemingly at random?
Good to know, I will give it a try. Does it still seamlessly switch when necessary?I don’t know if this cures the grid draw problem on yours, but I turned off seamless switch. And mine has not drawn from the grid any, when it’s not supposed too. And Jared changed some things on mine also.
It don’t know, this is what some one’s else on the forum said “4ms transfer turns into 20ms”. But I had to turn mine off, my ac couple inverter absolutely hates it. My 18Kpv and my ac coupled inverter would shut out together about 20 times a day. And a lot of time the EG4 monitor site would not catch it, because it would happen in the five minute snapshot window.Good to know, I will give it a try. Does it still seamlessly switch when necessary?
I've tried both ways and honestly can't tell a difference in switching speed. Maybe the EG4 guys will weigh inGood to know, I will give it a try. Does it still seamlessly switch when necessary?
@EG4_Jared ?Turning off seamless switch seems to have stopped the issue with the grid switching periodically although I still don't quite understand why (I'd prefer to have it enabled).
I'm now experiencing a new issue with PV installed yesterday. For several hours this morning everything was working great but starting in the afternoon PV started throttling and only powering loads with little or no power being used to charge the batteries. I have 2 Power Pro batteries and this was happening earlier when they were under 50% SOC. As I type this, they are sitting at 83% SOC with 0W going into them and all PV is throttled just to match loads. I've tried PV charge priority both on and off and it happens either way. What am I doing wrong here?
I have my AC coupling set up not to exceed my total net metering. Growatt tech told me if I had more solar panels than I needed, the Growatt could be limited. With RS485 CT meterWhen you set grid sellback, does it take AC couple into consideration, to not go over the limit, or is it just the PV on the 18 itself?
Nice! No chance I could use a Honda EU 3000 (120 V) generator, or two in parallel (?) On the generator input? Then I wouldn’t need the (unavailable) 2 chargeverters that I have on back order.Generator Boost with newest Firmware
Ok. But are you limiting the 18 as well?I have my AC coupling set up not to exceed my total net metering. Growatt tech told me if I had more solar panels than I needed, the Growatt could be limited. With RS485 CT meter
I have 12995 PV, 7140watts ac coupled and my export net meter is set to 6.5 kw. I should not get over 6.5 kw because I have 2kw of panels facing east. 2kw facing west and 3000 facing south. So usually I can see 4kw from ac couple and the PV curtailed to 2.5kw plus loads.Ok. But are you limiting the 18 as well?
My hope is that the 18 setting limits both it's own PV and the AC Coupled PV
The issue here is how the control system operates for each mode.Other threads have talked about the fact that in on grade mode when trying to do net zero, it’s really hard to control for large loads dropping off suddenly.
How does the 18 Kpv deal with large loads dropping off (or starting up) suddenly while in offgrid mode?
Doesn't this also mean that the POCO side measurement is also going to have some lag? Are they really this laggy / have poor high frequency response? I guess it depends on the specific CTs being used.The CTs are slow devices, you basically have to measure a half or even full cycle to know the current, more or less.
If the CTs are at the meter then yes. If the AC coupled inverter can’t/won’t throttle, that’s a different problem.I just want to know if the limit takes the AC couple into account when you set a limit?
Yes,.Appreciate all the thoughts, but I didn't ask how to limit my export, I just want to know if the limit takes the AC couple into account when you set a limit?