New to this forum and no knowledge about DIY solar system. a bit of background of my situation.
1. Purchased 15 panel used from Facebook market place. Qcell brand, 340 W, Voc 40.66 Short circuit 10.52
2. Ecoflow Delta Pro Ultra- Spec MPPT 1 (high Voltage PV) = 80-450 V, 15A, 4000W MPPT2 ( Low Voltage PV)= 30-150V, 15A, 1600W. It can input both at the same time

My question is

Series or Parallel? My thought is 2 set strings, all in series connection... HV PV= 10 to 11 Panels in Series which brings 4000 to 4400W and 400V to 440V LVPV = 3 Panels in Series = 1020W, 120V. 2 sets string will under 10.52 Amp. I will also install the circuit breaker Disconnect and 2 pole mini circuit breaker.. Higher Amp pass through, more danger?
Am I correct about my calculation and set up plan?

What makes me crazy is youtube video of the solar panel caught fire on the roof because of wrong installation, wiring, etc. That makes me chicken somehow.

many thanks
 

Attachments

  • Screenshot 2024-02-23 at 6.45.34 PM.png
    Screenshot 2024-02-23 at 6.45.34 PM.png
    314.1 KB · Views: 2
  • 4f50e105278f6fbb4b5b9aed39990cfe.jpeg
    4f50e105278f6fbb4b5b9aed39990cfe.jpeg
    178.1 KB · Views: 2
  • Screenshot 2024-03-19 at 9.43.35 PM.png
    Screenshot 2024-03-19 at 9.43.35 PM.png
    147.4 KB · Views: 2
Your math seems to check out. If you’re really concerned about fires it’s the wiring that you need to oversize and stay with 10 panels on your high voltage string and you should be set.

You need to do a precise or nearly precise calculation of the length from your solar panels to your DPU. Then use an awg current calculator to calculate the size of awg wire you need for the distance you need to run your cables. Go a size above what they recommend and you should be golden!
 