You stll need to fuse the inverter
you want to say fuse the cable to the inverter?
fuses are not for appliance protection
You stll need to fuse the inverter
FLIR 1 pro - wanted the higher resolution and extra mode.
Amazon.com
www.amazon.com
I just happen to have an old Galaxy A7 in a drawer so I can use it when testing things as the display.
Funny they still call it FLIR (Forward looking Infrared) - Seems like calling it a thermal camera might be more accurate these days. Especially with the color overlay verse the old black and white version.
My airplane had a FLIR turret - fly along and drop it out the belly and look around - had to be changed periodically when the liquid nitrogen inside leaked out. Back early 90's it was $250k a copy and my team replaced 1 of them 4 times. Good thing we had 8ft extender cables so we could hook the new one up in the aluminum can before install.
First 2 didn't work.... third one came with sea water sloshing around in the can and the 4th one worked.
Check out Uni-T.Ordering a different one.
What do you think the fuses are for? Or are you saying don’t use fuses?you want to say fuse the cable to the inverter?
fuses are not for appliance protection
Are you aware Batrius is not exactly 1 BMS for multiple parallel banks?because you need one BMS per bank, it may be that a cell on one bank gets a short circuit or simply slowly discharges towards 0V due to dentriden. if so, the other banks charge the remaining cells of the defective bank above 3.65V, it doesn't have to be such high currents, it already smells like 20A per bank, with 6 banks that's 120A so approx. 6kW that have to go somewhere.... you can't solve something like this with a fuse. each bank needs a BMS that is set as low as possible with the charging/discharging power. I have fused my banks with 100A and limited the respective BMS to 50A power, which is enough for 3x Multiplus 2 3000
That is great to hear that the insurance company actually does what they are supposed to do. What brand? Your experience is a good endorsement and counter to the usual horror stories.The fuse picture i posted was just an answer to the "what is a meltfuse" question.
The exact fuse was a mega 48v, 300 A.
The insurance is no problem.
Oooh, I know this one: Both!Which do you think may fail closed? FET or NO contactor?
My guess is the alarm thought it was a meter of steam. I hope this fail is reported and the Nest folks are able to correct what clearly went wrong.Google is investigating this btw
If you are in the US, the Federal Trade Commission would also like to know about this. But for the fortunate waking of your son, this equipment failure was headed to fatalities. There needs to be a recall here.Google is investigating this btw
Ah, from the comfort of our armchairs, we are all fire investigation experts.We may never know, but I see a lot of sloppy heat shrink on/under some of these lugs.
![]()
Don't stress too much. People love to solve a riddle whether it be a crime, a plane crash or a house fire. And every last one of us feels entitled to be an expert in the process. I see the same thing, but 10 x worse, on AVherald.com where every single person completes the aircraft crash analysis and offers a final report before the embers even cool. Your transparency and data sharing has been invaluable and has and will continue to provide many with excellent insights.Guys, please, yall looking at things way too far. The shelves were fine, the fire fighters have torn everything apart to drag all the cells outside. I dont even know what is being discussed here.
Here in Europe has a 3 Phase System 400V. Single Phase is 230V.@D71 Did you account for 3 phase? 16A X 230V X 1.73 (3-ph) =6,366W = 6.37KW
I threw it online calculator@D71 Did you account for 3 phase? 16A X 230V X 1.73 (3-ph) =6,366W = 6.37KW
The OP Victron inverters are 230vac units for his 3 phase configurationHere in Europe has a 3 Phase System 400V. Single Phase is 230V.
When connecting 3 230v (L-N) inverters in a wye configuration you get 400v when measuring L-L.The OP Victron inverters are 230vac units for his 3 phase configuration
Same math different voltage so, 16A X 400V X 1.73 =11.072 so, math good & data bad.I threw it online calculator
i knew the 3 phase in Europe are advertised as 11kW right before posting.
Put in delta vs wye
These are wye applications
View attachment 215733
View attachment 215732
View attachment 215735
Show me where I am wrong. It is careless work and in a later post the OP says he had to fix that. I don't know of any inspector that would pass it.Ah, from the comfort of our armchairs, we are all fire investigation experts.
Yes, Batrium would recommend a contactor per string. In the OPs case he chose to use one single contactor, beyond the seven mega fuses.Are you aware Batrius is not exactly 1 BMS for multiple parallel banks?
There is a supervisor: Watchmon Core.
There are K9s: The actual BMS.
For instance, If you have six parallel banks, you need six K9s and one Watchmon Core. The six K9s talk to the supervisor over CAN, reporting battery parameters.
This BMS design uses contractors to control the system. You can have contactors between each bank so you can disconnect the faulty bank in a critical event. There is no chance any cell can be charged over 3.65V except when your contactors fail closed.
Which do you think may fail closed? FET or NO contactor?
I'm more concerned about his fuse holder setup. What is the backer they are attached to? I've also seen mention that "Victron recommends this fuse". Well, yes, but you also have to look at how they are installed.Honestly, I had 5 of the 58V-rated ones (clear package) and I thought they were fine, until this House Burned Down thread.
The OP appeared to have them, so I upgraded to the 70v MEGA.
2.5 kA AIC at 70v (littelfuse sf51) is better than 1 kA AIC at 58v (littelfuse bf2)
I would never use MEGA for a battery, just for inverters and MPPTs.