Battery connector cables

AWG 4 is not safe for 250 amperes. You need Marine Grade 1/0. Some times that is hard to find so 2/0. Blue Sea Circuit Wizard is a much better calculator.
 
You need Marine Grade 1/0
@wyattamdahl
Unless this is on a boat or possibly in some environment that is conducive to corrosion you don't need marine grade wire.
2/0 awg is right on the edge of what you need.
You could go bigger.
How did you determine you require 250 amps?
 
What you should use is fine stranded pure copper with insulation rated to 105 celcius.
Quality welding cable fits the bill nicely.
 
@wyattamdahl
Unless this is on a boat or possibly in some environment that is conducive to corrosion you don't need marine grade wire.
2/0 awg is right on the edge of what you need.
You could go bigger.
How did you determine you require 250 amps?

if i was to be running everything at once it would be around 230 amps. So i rounded up to 250
 
The very best welding cable has 90 deg c insulation. Using welding cable you have to "size up" from recommended marine cable AWG. Marine cable, from quality supply house, is Coast Guard required for any marine use and is consistent in its quality. We throw the dice when buying welding cable, the actual quality can vary. I am not saying you can't use welding cable. Just that marine grade is better and the same cost or less. 1/0 marine is the exact awg you need. I use 2/0 cable from Genuine Dealz. https://www.genuinedealz.com/products/custom-battery-cable-marine-grade-by-the-foot
 
I had some 2/0 welding cable that was premium quality. The insulation split lengthways. I switched to marine grade and don't look back. :)
 
My point is welding cable is fine if the wire you bought from Amazon by some accident was premium wire. Check some of the stuff sold by Bob's Curbside Welding Supply.
I use marine standard as it is the same quality from my 2 or 3 suppliers. The marine grade 105C dry, 75C wet, with a UL stamp. Then I know what is going down the road.
 
What cable strippers should you use with these cables? The one I have has the blade stick out that you adjust to cut the insulation but there is nothing to stop it from cutting the conductor itself unless you have it precisely adjusted. For the stiff cables this doesn't cause an issue but for these cables I'm sure it would cut those thin wires.
 
For my stationary application I am using these wires with mechanical lugs.
When bent it stays bent.
It also tends to stand off the backing board without assistance.
For 1 awg - 2/0 awg I like https://www.servicewire.com/Products/XH-CT.htm
For <1awg I like stranded thhn which is cheap and readily available at your nearest big box store.
The biggest problem is that 2/0 awg of either is pretty hard to cut.
I strip it with my high leverage cutters without issue.
 
What cable strippers should you use with these cables? The one I have has the blade stick out that you adjust to cut the insulation but there is nothing to stop it from cutting the conductor itself unless you have it precisely adjusted. For the stiff cables this doesn't cause an issue but for these cables I'm sure it would cut those thin wires.

I score the insulation by gently gripping with wire cutters and swinging them around the cable. Or a razor blade.
Then I bend the cable and watch it split open at the cut.

If you lose a few strands that isn't a huge issue. The remaining copper can carry the current, and after some distance of contact, current will spread into the cut strands so all cross section is used and IR drop is kept low.
 