I think Precharge resistors are fine but I just don't like the way it was implemented in the EG4. I appreciate the fact that they were trying to make something that was more automated but it just seems like it did not work out.I’ve wondered the same thing.
And since this is usually a one time event I would prefer a battery without all the precharge nonsense built in (like my old style GYLL) so I could just use a $2 resistor one time and get on with my life.
It seems the precharge circuitry might be more trouble than it’s worth ?
Just one opinion.
50V/50 ohm = 1A, 50V^2/100 ohm = 25W, probably works fine for precharge.
Say 5V drop (leaving 45V to power inverter) divide by 50 ohm = 0.1A, 45V x 0.1A = 4.5W, not enough to keep inverter up with standby draw.
You'll need to close switch fast enough to supply inverter before it starts inverting.
Consider 100A, 50V. That's 0.5 ohms. 400A would be 0.125 ohms. Look for a piece of wire in that range, and heavy enough to carry a couple amps or more. That would precharge capacitor without exceeding BMS limit, and carry 100W or more of idle consumption. 12 awg is 0.16 ohms per 100'. Have a 100' or 250' coil of Romex? About 0.3 ohms or 0.75 ohms round trip. Put a wire nut on white & black at one end. use other end as precharge resistor. That should limit current to 75 or a couple hundred amps and power up the inverter.
@upnorthandpersonal that makes sense, except in most cases with Lithum batteries with BMS, the Battery is what can't handle the inrush and is damaged if the inverter isn't pre-charged. So they are putting pre-chargers in them to try to protect their BMS and battery, not for the inverter necessarily.
I think the problem with all this is that Signature Solar does not design and manufacturer their own BMS's. They may not be able to modify the surge over-current time and level. Please, Signature Solar, correct me if I am wrong. It is hard to say from their web site and videos how this all works
But if S.S. puts the BMS and battery system together, they may be able to mate up a BMS that has a higher instantaneous current limit rating.
I do not see a surge rating on their specs. Continuous discharge is, I think, 200 amps and recommended is 60 amps.
Charging a capacitor like these inverters use can draw hundreds of amps momentarily. Might be difficult to get that protection just right, and for all of these different inverters too. But, it must work. Some pre-charging can help but I don't think that one resistor value is going to work for all inverters out there.
https://upload.wikimedia.org/wikipedia/commons/1/1b/Capacitor_charging_Current_and_Voltage_Graph.png
And "Closed loop" inverter/charger to BMS is a great thing but I don't think it is something that can help with something like this. It might help to let the BMS what to expect though the next time it turns on ?
Hedges: Would a heavier gauge of wire be better in this situation? Like 10g? Just asking out of curiosity.
I'm repeating myself here, but in my opinion, the capacitor pre-charge should be part of the inverter design. ... Doing it on the battery can lead to all kinds of weird compatibility issues and edge cases that cause the pre-charge to be completely ineffective.
My theory is 2 different types of inverter, 1 that will run without a battery and 1 that must have a battery.All we need from the inverter is to not turn on immediately. Either manual precharge or BMS doing it, we want capacitors to reach near full voltage and then switch closed for low resistance before inverter starts sucking multiple amps.
Nope, they don't make these, or even assemble them. They just unload containers of them, shipped from China.
At 38 degrees and colder I reduce Charge Max to the XW6848 to limit to 50 watts. Normally charge max is 2500 watts for me. Batts are 280 ah Eve cells.Well good deal. The batteries did their job and kept you from destroying them by charging while below freezing. 41 is pretty cold, I hope you have enough heat to keep your batteries from freezing on a regular basis.
I'd simply put a voltmeter at the DC terminals on the inverter and SEE what happens at the instant of turn on.Sure, you could use any gauge, even 4/0 if long enough to provide the desired resistance.
All we need from the inverter is to not turn on immediately. Either manual precharge or BMS doing it, we want capacitors to reach near full voltage and then switch closed for low resistance before inverter starts sucking multiple amps.
The reason inverter can't easily do this is it doesn't have a controlled switch between DC input and capacitors. Some have a breaker built in, some do not.
BMS has FET or relay between cells and battery cables. Simply turning on FETs gradually so they present high resistance (limiting current) and burn off some heat due to voltage drop (as high as 48V or so) times current. Given enough time, that fully charges capacitors in inverter. Trouble is, inverter will likely draw some current for its internal circuitry, so FET (or separately switched precharge resistor) needs to handle that current. Definitely can't have inverter start producing AC until precharge complete and FET on hard or relay closed.
Best design would be BMS performs precharge and communicates to inverter saying when it is OK to turn on.
Specs for Sunny Island are 4W standby, 25W idle. (Of course, if AC loads present and motors being started, could be 11kW)
4W/48V = 83 mA. Sunny Island powers up in Standby, until you press and hold button to start.
25W/48V = 0.52A, this is what it would draw if AC loads were disconnected and inverter started the moment voltage appeared.
(Problem with other inverters is likely that they power up when DC appears.)
For this inverter, need to design for 83 mA.
Using a wire for precharge resistor, could be a length of telephone or LAN wire, enough for a few ohms or a fraction of an ohm.
That wouldn't be able to power inverter if it turned on before you closed the switch.
Using 12 awg or something larger, enough for about 0.5 ohms, could power inverter up to a few amps (couple hundred watts) with a few volts drop. If switch closed with a few amps and a few volts across it, small inrush. Best to close before that happens.
Don't use a coil of single wire, that is inductance. A coil of 2-wire cable is fine, with the two wires joined at end; current flows out one way through coil and back the other way, cancelling magnetic field and inductance.
I do the gateway from S/E and XanBus to xw6848. Modbus works thru port 502 on the LAN. My JKBMS is bluetooth, That reading comes from a raspberry pi zero to the wifi LAN.Without a Growatt inverter or a laptop not sure what you will hook the RS485 cables too. My understanding is the batteries don't talk to each other, but can be configured to be polled thru the RS485 by compatible inverters. Right now that's just Growatt inverters.
I took all the RS485 cat5 cable jumpers off mine. I hooked my laptop to each of them to check the BMS and voltages, but there's nothing to set, just monitor if you want.
I have the Schneider Gateway also, hooked to my XW Pro 6848 and MPPT 60 via Xanbus. That all communicates well. I know the gateway has RS485 and supports modbus, but my understanding is the EG4 batteries do not communicate with it for whatever reason. It would be great if they did or if there was way to facilitate that. Having SOC controls in the XW would help.I do the gateway from S/E and XanBus to xw6848. Modbus works thru port 502 on the LAN. My JKBMS is bluetooth, That reading comes from a raspberry pi zero to the wifi LAN.
English? I mean seriously, who needs their anything (mppt) to talk in French?So, what "standard" are you guys using to talk with all of these lithium BMS's from invertter/chargers?
English? I mean seriously, who needs their anything (mppt) to talk in French?![]()
I'm sure S/E makes backroom deals with the battery system manuf. S/E won't step on their toes and vice-versa. So the customer is left without solutions without lots of $$$ spentI have the Schneider Gateway also, hooked to my XW Pro 6848 and MPPT 60 via Xanbus. That all communicates well. I know the gateway has RS485 and supports modbus, but my understanding is the EG4 batteries do not communicate with it for whatever reason. It would be great if they did or if there was way to facilitate that. Having SOC controls in the XW would help.
Unfortunately, looking at how the BMS communication is selected from a specific list of batteries in the XW Insight Home and not a more generic communication like used by other inverters, make me think you are right. I'm not going to hold my breath, but it would be in BOTH their best interest to be communicate with each other.I'm sure S/E makes backroom deals with the battery system manuf. S/E won't step on their toes and vice-versa. So the customer is left without solutions without lots of $$$ spent
So, what "standard" are you guys using to talk with all of these lithium BMS's from invertter/chargers ?
I'd like to say I am shocked, but this is what I said early on in this thread.In the AltE Schneider XW Webinar today ... It was clear by his answer, they only plan on supporting batteries with "mutual interest".