I thought the OP was running 120/240 volt split phase air conditioners...?An inverter that can invert to split phase is not required for this implementation.
There are no line to line loads.
If they are using the Victron programming system VE connect, the sycronization is probably done through VE connectI don't see any ethernet cable between the inverters so I'm guessing they are not synchronized.
There must be some misunderstanding.A 120/240 split phase device will NOT run on 120/208 WYE volt split phase, The neutral is not in phase.
There must be syncronization of some matter, probably they didnt show that detail.
I was under the impression that they are both 120VAC.I thought the OP was running 120/240 volt split phase air conditioners...?
Via an ethernet cable, no?If they are using the Victron programming system VE connect, the sycronization is probably done through VE connect
Is VE connect over ethernet?The synchronizing data can be transferred many ways, I would think that VE connect could handle that within the VE connect cabling,
Sorry, UTP cable.Is VE connect over ethernet?
Did not understand that they were 120 volt air conditioners, people using two inverters are more likely to use split phase, I assume....The panel does not have L1 and L2 interleaved so you can't have a double pole breaker.
Air conditioner 1 is on the left side of the panel on a 20 amp breaker and air conditioner 2 is on the right side of the panel on another 20 amp breaker. So I conclude they are 120VAC units.
I havent gone back to the Victron site, I read traditional schematics, not at all used to block diagrams such as Victron uses, That is not the standard in the industry.Sorry, UTP cable.
Do you see one?
I have no doubt the higher layer protocols are proprietary but the I suspect the cable with be cat 5 or higher un-sheilded twisted pair.VE connect seems to be properity Victron, My Victron Skylla -TG chargers are pre Victron connect
Thus endeth the tempest in a teacup?Thin blue trace VE connect from the inverters to the Cerbo logic unit, does seem to be RJ-45 connectors
Peaking at what?OK, peeking at it again, they are labeling it VE direct