I just used the regular Ethernet cables provided. Plugged into the CAN port.Can you please tell me the pin layout you used of the cable between the MR & the Jakiper?
I just used the regular Ethernet cables provided. Plugged into the CAN port.Can you please tell me the pin layout you used of the cable between the MR & the Jakiper?
Further example, if I have the battery disconnected the PV will dump full current into my loads which currently I am just running my garage so little to no usage, the rest of the power is returned to the grid. When the batteries are connected, all bms info is displayed on the inverter correctly. Once again it will power the loads and charge the batteries. Once full, the inverter will go down to almost 0 current and then limit the PV input. I have tried this on batt priority, self consume, eps on and off. I am still running the original firmware.So I just found a snag. It seemed like everything was working fine until the batteries were fully charged. Then the inverter limited the PV input instead of putting the power back to the grid. Can anyone tell me if there’s a setting I am missing to achieve this?
I would love to go through the menu's and get a good explanation of each setting. I have downloaded most manuals of all MR clones and they basically have all the same text, but not a good explanation.Further example, if I have the battery disconnected the PV will dump full current into my loads which currently I am just running my garage so little to no usage, the rest of the power is returned to the grid. When the batteries are connected, all bms info is displayed on the inverter correctly. Once again it will power the loads and charge the batteries. Once full, the inverter will go down to almost 0 current and then limit the PV input. I have tried this on batt priority, self consume, eps on and off. I am still running the original firmware.
technically 80% DOD (depth of discharge) should be allowed, but I would limit it to 75% .What would be the recommended disc depth setting?
argghh... this unit is really something....
My batteries were relatively easy to fill it seems. And once they were full the MR continued to feed back into the gridFurther example, if I have the battery disconnected the PV will dump full current into my loads which currently I am just running my garage so little to no usage, the rest of the power is returned to the grid. When the batteries are connected, all bms info is displayed on the inverter correctly. Once again it will power the loads and charge the batteries. Once full, the inverter will go down to almost 0 current and then limit the PV input. I have tried this on batt priority, self consume, eps on and off. I am still running the original firmware.
I honestly tried. I had a celeron linux laptop with only 4GB ram , i installed a virtual win10 machine. could only give it 3GB ram, 1 core . slow as in typing speed was terrible. But the program worked. Once it gave an error while flashing, retried and it went through without a hitch.Firmware arm: v1.03.06 DSP: v1.04.06
Your settings are pretty identical to mine but there isn’t a discharge current setting with this firmware.
I think you are correct with the D and C induction.
I should just update the firmware but I’m a little reluctant, with how things go with this inverter that I’ll brick it.
AbsolutelyMaybe I’ll try that tomorrow.
So when your battery bank is full, you are pushing full PV current back to the grid?
These are my ASCII settings from the pictures I took from my settings menu:So when your battery bank is full, you are pushing full PV current back to the grid?
ARM: V1.03.12
DSP: V2.04.12
SETUP
1. -- SYS SETTING --
1: WORK MODE -> 1. SELF CONSUME
2: EPS ENABLE -> 2. ENABLE
3: BAT WAKE-UP -> 2. ENABLE
4: REMOTE CTRL -> 2. ENABLE
5: START DELAY -> START-UP DELAY INPUT: 20 UNIT: SEC
6: PV INPUT -> 1. INDEPENDANT (I have 3 mppt's in use with 3 different arrays)
7: Anti Reverse -> 1. DISABLE
8: ARC ENABLE -> 1. DISABLE
9: BUTT ENABLE -> 1. DISABLE
2. --BAT SETTING--
1: BAT TYPE -> 3:Lithum
2: DISC-DEPTH -> GRID DOD: 080% OFFGridDOD: 080% Return: 040% (not sure what the return means)
3: CHARG-CURR -> INPUT: 045 UNIT: A
4: BAT-COMM -> 2: CAN
3. --GRID STD-- -> 9:US-CA ( I assume short for USA-CANADA?)
4. --GRID SET-- -> 2: 120V/240V
5. RUN SETTING -> 1: REACT MODE -> 1. POWER FACTOR -> 1.0
2: GRID POWER -> -GRID PERCENT_ INPUT: 090%
3: DISC POWER -> -DISC PERCENT- INPUT: 100%
4: PV POWER -> -PV PERCENT- INPUT: 100%
5: VAC-MIN -> -GRID VOLT LOW- INPUT: 150 UNIT: V
6: VAC-MAX -> -GRID VOLT HIGH- INPUT: 280 UNIT: V
7: FAC-MIN -> -GRID FREQ LOW- INPUT: 57.0 UNIT: Hz
8: FAC-MAX -> -GRID FREQ HIGH- INPUT: 63.0 UNIT: Hz
9: ACTIVE REP. -> -ACTIVE TYPE-
1. PWR-VOLT RES -> -PWR-VOLTAGE- -> 2. ENABLE
2. PWR-FREQ RES -> -PWR-FREQUENCY -> 2. ENABLE
3. PFC-VOLT RES -> -PFC-VOLTAGE- -> 2. ENABLE
4. PFC-FREQ RES -> -PFC-FREQUENCY -> 1. DISABLE
5. ACTIVEISLAND -> -ACTIVEISLAND- -> two options: 1.DISABLE 2.ENABLE no option highlighted, i will leave it that way ;-)
6. Leack Curren -> -Leack Dete- -> 1. DISABLE
7. Insulation d -> -Insul Dete- -> 1. DISABLE
6: 485 ADDRESS
7: BAUD RATE
8: LANGUAGE
9: BACKLIGHT
10: DATE/TIME
11: CLEAR REC
12: PASSWORD
13: MAINTENANCE
14: FCTRY RESET
15: PARALLEL
I don't think it will hurt to upgrade your firmware.I do not have many of those menu’s you have. This is the ones I have with this firmware.View attachment 110207
But you can roughly compare then and hightlight the differences between your & my settings?I do not have many of those menu’s you have. This is the ones I have with this firmware.