Need help with PowMr 3000W 24V Solar Inverter Charger parameters settings

@Chri5co63 I am going to set my CHINS to the parameters in post #23 because they look more realistic than the defaults and I will let you know what happens.
 
If all 12 panels are connected in series then amps =9.02a, voltage = 21.6v x 12=264v w=2381

But if I have interpreted what you have said above
If they are connected 6 strings of 2 in parallel=
2 in series =9.02a,voltage =2 x 21.6v=43.2v
then 6 in parallel =9.02 x 6= 54a, voltage =43.2v w=2332

In the listing above it suggests max charge amp from inverter to battery =02c =40a... 20% of a 200ah battery. Your peak solar pv output is 54a. at 43.2vdc available to the inverter
This is our setup with connections as shown (less the separate inverter and charge controller as we’ve replaced those with the on MrPow inverter charger…
IMG_9077.jpg
 
Last edited:
  • Like
Reactions: mib
It seems to me that we are talking about AIO SRNE, this is a manufacturer, powmr brand


my version is 220 volt
IMG_20230211_174958.jpg
it says here, the maximum current from the panels is 40 amperes

2s6p you get 54 amps which is more than 40 amps

maybe 3s4p is better for you

also note there is a maximum pv power parameter of 1600 watts, which is less than 2332 watts

Are your solar panels already connected?

i also want to go over 1600 watts, my panels are 595 watts in a 2s2p circuit i fit into 80 volts and 36 amps, 2380 watts

IMG_5898.jpg

but i have feelings about it :)
 
It seems to me that we are talking about AIO SRNE, this is a manufacturer, powmr brand


my version is 220 volt
View attachment 135182
it says here, the maximum current from the panels is 40 amperes

2s6p you get 54 amps which is more than 40 amps

maybe 3s4p is better for you

also note there is a maximum pv power parameter of 1600 watts, which is less than 2332 watts

Are your solar panels already connected?

i also want to go over 1600 watts, my panels are 595 watts in a 2s2p circuit i fit into 80 volts and 36 amps, 2380 watts

View attachment 135187

but i have feelings about it :)
The following is a link for the manual for our PowMister Solar Charger.
One can find on pp. 31-32, the Technical Specifications. The listed Maximum Input Current is 60A and the PV Charging Current Range is 0-60A.


The following is a picture of the label on one of our solar panels...

IMG_4428.jpg
 
  • Like
Reactions: mib
Energy Miser
Mark Durrenberger’s Blog — writing about homes and energy.

What Does Solar “Inverter Clipping” Mean?​

November 2, 2017
The short answer is that “inverter clipping” means your solar inverter is limiting slightly the amount of electricity going from your solar energy system into your household for use, because it reached its maximum capacity.
Here’s a longer explanation.
For background you should know that, like solar panel ratings, inverter ratings are approximate. Many inverters can convert more DC power (from your panels) to AC (for use in your home or business) than their model numbers imply. For example, the maximum power output of the SolarEdge SE7600A is actually 8,350 watts, according to the manufacturer. So the inverter has no problem handling up to 8,350 watts of capacity at a time.
If the panels are operating at a capacity that exceeds the inverter’s capacity, “clipping” occurs. The inverter trims the output to the maximum it can handle and you lose a little production. This graph shows a customer’s production with clipping at the top of the curve.

Reference above "clipping" If the panel output is greater than the inverter spec......
 
  • Like
Reactions: mib
The following is a link for the manual for our PowMister Solar Charger.
One can find on pp. 31-32, the Technical Specifications. The listed Maximum Input Current is 60A and the PV Charging Current Range is 0-60A
I have exactly the same instruction, but on the side panel of the AIO there are these 1600 watts and 40 amps

can you take a photo sticker of your AIO's specs?

do you already have everything working? and you want to change only the battery or the system is just planned?
 
Energy Miser
Mark Durrenberger’s Blog — writing about homes and energy.

What Does Solar “Inverter Clipping” Mean?​

November 2, 2017
The short answer is that “inverter clipping” means your solar inverter is limiting slightly the amount of electricity going from your solar energy system into your household for use, because it reached its maximum capacity.
Here’s a longer explanation.
For background you should know that, like solar panel ratings, inverter ratings are approximate. Many inverters can convert more DC power (from your panels) to AC (for use in your home or business) than their model numbers imply. For example, the maximum power output of the SolarEdge SE7600A is actually 8,350 watts, according to the manufacturer. So the inverter has no problem handling up to 8,350 watts of capacity at a time.
If the panels are operating at a capacity that exceeds the inverter’s capacity, “clipping” occurs. The inverter trims the output to the maximum it can handle and you lose a little production. This graph shows a customer’s production with clipping at the top of the curve.

Reference above "clipping" If the panel output is greater than the inverter spec......
Aha. Nice article! In another...
"Inverters are most efficient when running at or near full capacity. Going up an inverter size, for example installing an SE-10,000 inverter with a 7,500-watt system, would make the system less efficient. The lost production in that scenario would be more than the little bit of production lost from occasional clipping.
Makes me wonder if our inverter is too large compared to the PV Input wattage.

Put another way, the choice is lower efficiency 365 days a year, or very high efficiency year-round with occasional clipping. You get considerably more solar production in the second scenario." - (Mark Durrenberger’s Blog — writing about homes and energy.)

It seems to me that we are talking about AIO SRNE, this is a manufacturer, powmr brand


my version is 220 volt
View attachment 135182
it says here, the maximum current from the panels is 40 amperes

2s6p you get 54 amps which is more than 40 amps

maybe 3s4p is better for you

also note there is a maximum pv power parameter of 1600 watts, which is less than 2332 watts

Are your solar panels already connected?

i also want to go over 1600 watts, my panels are 595 watts in a 2s2p circuit i fit into 80 volts and 36 amps, 2380 watts

View attachment 135187

but i have feelings about it :)
Yes, the solar panels have been connected since last summer. We connected them according to the Eco-Worthy Kit setup instructions.
 
  • Like
Reactions: mib
I don't think it overly matters if the panels give out a little more than the inverter is rated at ,,,, possibly up to 20% but it is important you are aware of it. Especially If like in the Uk there is little chance of achieving maximum solar output.
 
or very high efficiency year-round with occasional clipping
that's exactly my goal
I don't think it overly matters if the panels give out a little more than the inverter is rated at ,,,, possibly up to 20% but it is important you are aware of it. Especially If like in the Uk there is little chance of achieving maximum solar output.
1600/2400 turns out 50% but is fully invested in the parameters for both current and voltage

but you calmed me down a bit :)
 
i plan to do the following settings for lifepo4 140 ah 24 voltss battery

04 26 (3,25) v
05 26,4 (3,3) v
07 40 amper
08 USE
09 Boost charge - 27,6 (3,45) v
10 Boost charge time - 120 min
11 Floating charge - 27,6 (3,45) v
12 Over discharge voltage - 24 (3) v
13 Over discharge time - 30 sec
14 Under voltage alarm - 24,8 (3,1) v
15 Discharge limit - 24,4 (3,05) v
17 Equalization voltage - 27,6(3,45) v
28 Max AC charger current - 10 amper
35 Undervoltage recovery - 25,6 (3,2) v
36 Max PV charger current - 40 amper
37 fully charged recovery - 26,8 (3,35) v

my goal is to use the battery as little as possible, during normal times, to save it during city grid outages
 
I have exactly the same instruction, but on the side panel of the AIO there are these 1600 watts and 40 amps

can you take a photo sticker of your AIO's specs?

do you already have everything working? and you want to change only the battery or the system is just planned?
The system has been up and running (charging 4 12v Lead Acid Gel batteries connected in 2S/2P for 24v) since las summer. At this time, we are only replacing the batteries with 4 Chins LiFePo4 12v 200AH batteries connected in 2S/2P for 24v.

Currently, I am not at the cavin where the solar array is, so I cannot supply you with a photo of the side sticker. I believe you can find the same information on pages 31-32 in the manual in the following link:


(i.e. In the above manual, on page 32, under the Solar (PV) Charging section, it reads Max Input Power as 1400w and Maximum Input Current as 60A)

However, When I look up the inverter on Amazon (where it was purchased), I find the following photo (not of the sticker, but "brochure"):
IMG_9079.jpg
 

Attachments

  • IMG_4428.jpg
    IMG_4428.jpg
    18.1 KB · Views: 12
  • Like
Reactions: mib
i plan to do the following settings for lifepo4 140 ah 24 voltss battery

04 26 (3,25) v
05 26,4 (3,3) v
07 40 amper
08 USE
09 Boost charge - 27,6 (3,45) v
10 Boost charge time - 120 min
11 Floating charge - 27,6 (3,45) v
12 Over discharge voltage - 24 (3) v
13 Over discharge time - 30 sec
14 Under voltage alarm - 24,8 (3,1) v
15 Discharge limit - 24,4 (3,05) v
17 Equalization voltage - 27,6(3,45) v
28 Max AC charger current - 10 amper
35 Undervoltage recovery - 25,6 (3,2) v
36 Max PV charger current - 40 amper
37 fully charged recovery - 26,8 (3,35) v

my goal is to use the battery as little as possible, during normal times, to save it during city grid outages
what are parameters 04 and 05
 
  • Like
Reactions: mib
I do like all the responses to the posts on this thread, not only is it helpful to me and my situation, but probably somewhat to each of you to some degree. The more I read and study, the more intrigued I become and the more I realize that their is no limit to all the possibilities in solar energy production.
what are parameters 04 and 05
04​
Battery Power to Utility Setpoint​
23.0V (Default)​
Setting voltage point back to utility source when selecting “SBU” in Program {01}. When the voltage of the battery is lower than this setting, the output switches from inverting to the utility (generator). The setting range is from 22c – 26-v in 0.2v increments.​
05​
Utility to Battery Power Setpoint​
{05} 28.0v (Default)​
Setting voltage point back to battery mode when selecting “SBU” in Program {01}. When the battery voltage is higher than the setting value, the output is switched from the utility to the battery mode. The setting range is 24V – 30V, in 0.2V increments * Cannot be higher than setting in {14}​
...according to the manual, that is.
 
  • Like
Reactions: mib
The CHINS Inverter started doing weird things so I set it back to where it was. It appears that my batteries, TCBWorth, don't like those settings. I have tried to get the parameter info from them but got no response.
 
My inverter shows battery 24.9v now. (15% capacity) but my battery has still got 46% capacity ... my BMS shows 3,15v per cell (x8)=25.2v (100ah 24v )
Because my inverter is on battery load the voltage drops dependant on variation in the load.
So the inverter is showing the battery voltage under load and not battery capacity left in AH's

Therefore I think (26) 3.25v on the inverter is high probably still got 60ah left in the battery
 
Last edited:
The CHINS Inverter started doing weird things so I set it back to where it was. It appears that my batteries, TCBWorth, don't like those settings. I have tried to get the parameter info from them but got no response.
Like I said previously, I am impressed and grateful with the correspondence from Chins. Not so much with PowMr, as the only response I received was to set the Battery Type as "User". Big Deal ?
 
@LSC I have the same situation in my new, first experimental system ("P28 is coming from the grid and it is only tied to a 20A breaker right now."). So, I set the max current to 20A thinking it is the limit on the current taken from AC. But I found it was taking for ever to charge the battery (I shut it off since my solar panels, used ones from Santander, had only OC of 32.4V and op. vol. of 28.4 and was not charging as MPPT vol range was 30 to 100. But then when I put two in series, still it did not charge and vol total was only 32.4V. My panels are on the ground with shadows from building etc.). So, I am wondering if this number (that you and I set as 20A), refers to the battery charging current OR the current drawn from the AC. Right now, I have just two 12.6 vol LiFeP4 batteries in series, each, 100 Ah (Eco-Worthy batteries). -- So, at 20A battery charging current, two batteries should have been charged in 10 hours. And at 20A grid current, just two hours (approximate - You have RMS value for the AC etc.) which did not happen.
So, 20A is AC current or DC battery charging current? TIA
 
Thank you guys for this post. I’m new and following as I have just set up a 3000 watt Powmr system. No pv yet but 2 100ah batts. I’m just trying to follow one of y’all’s setups and get my feet wet into all this new technology. Thanks will continue to follow and hope to get the right setting for me.
 

Attachments

  • IMG_5845.jpeg
    IMG_5845.jpeg
    151.1 KB · Views: 4
I have recently purchase a similar unit from them. Can take much more input for panels.
Just read thru the thread, great info. When I went thru my manual, some setting did not match the inverter settings. I adjusted some based on this thread, will be looking at others over the next few days. Total newbie here.
4@330w 36v panels. In series
POW-LVM3K-24-H
4 @ 12v 100 ah 2S2P
This inverter needs a minimum of 150v or 120v by manual.
Now I need some sun, so I can see more smartness logging!
 

Attachments

  • image.jpg
    image.jpg
    149.1 KB · Views: 1