Hello,
I am hoping some Schneider Conext XW Pro experts can help me with a problem.
Short summary: I have an XW Pro connected to the grid, and it is primarily a battery charger. I have two other XW Pros supplying power from batteries. I have EG4-LL batteries and BMS communication is working.
The Charger XW Pro is charging at night and I cannot figure out why. Here is the nighttime battery chart:
![1687952557500.png 1687952557500.png](https://diysolarforum.com/data/attachments/154/154741-2acc29e355113a841bd1561aa9791c55.jpg)
It started charging at 12:19 am:
![1687952621530.png 1687952621530.png](https://diysolarforum.com/data/attachments/154/154742-7686fe8f769ebb0dbcaddd659da158b4.jpg)
It stopped when the batteries were at 50% charge. This parameter I understand. The High SOC Cutout is set to 50%. It happened again at 2:47 am.
![1687952701837.png 1687952701837.png](https://diysolarforum.com/data/attachments/154/154743-128d88dc8e324434c4c776cabfbdd87e.jpg)
I think it is starting the charge because of two possible reasons: the SOC touches 45% or maybe the battery voltage drops to 52.4V.
These numbers are nowhere in the inverter settings.
![1687952854637.png 1687952854637.png](https://diysolarforum.com/data/attachments/154/154744-cd557456ca96f6aafa4f9201b36d3ed4.jpg)
![1687952896154.png 1687952896154.png](https://diysolarforum.com/data/attachments/154/154745-0aec30c0c682eb010ebb1ed0d71a98e6.jpg)
I have seen some really good comments from Schneider experts. This has me baffled. What am I missing? Also, these are the Charge Controller settings.
![1687953021813.png 1687953021813.png](https://diysolarforum.com/data/attachments/154/154746-289c3cec9f27af81a8911dde6b29760f.jpg)
The Charge Controller MPPT 100 600 seems to have no communication with the BMS. I am surprised there is no setting for Li-on batteries.
![1687953106861.png 1687953106861.png](https://diysolarforum.com/data/attachments/154/154748-ee26f83e421a1a943c43fefbc8aee18d.jpg)
I appologise for the long post, but hopefully some wizard can scan my settings and point out any obvious errors.
I am hoping some Schneider Conext XW Pro experts can help me with a problem.
Short summary: I have an XW Pro connected to the grid, and it is primarily a battery charger. I have two other XW Pros supplying power from batteries. I have EG4-LL batteries and BMS communication is working.
The Charger XW Pro is charging at night and I cannot figure out why. Here is the nighttime battery chart:
![1687952557500.png 1687952557500.png](https://diysolarforum.com/data/attachments/154/154741-2acc29e355113a841bd1561aa9791c55.jpg)
It started charging at 12:19 am:
![1687952621530.png 1687952621530.png](https://diysolarforum.com/data/attachments/154/154742-7686fe8f769ebb0dbcaddd659da158b4.jpg)
It stopped when the batteries were at 50% charge. This parameter I understand. The High SOC Cutout is set to 50%. It happened again at 2:47 am.
![1687952701837.png 1687952701837.png](https://diysolarforum.com/data/attachments/154/154743-128d88dc8e324434c4c776cabfbdd87e.jpg)
I think it is starting the charge because of two possible reasons: the SOC touches 45% or maybe the battery voltage drops to 52.4V.
These numbers are nowhere in the inverter settings.
![1687952854637.png 1687952854637.png](https://diysolarforum.com/data/attachments/154/154744-cd557456ca96f6aafa4f9201b36d3ed4.jpg)
![1687952896154.png 1687952896154.png](https://diysolarforum.com/data/attachments/154/154745-0aec30c0c682eb010ebb1ed0d71a98e6.jpg)
I have seen some really good comments from Schneider experts. This has me baffled. What am I missing? Also, these are the Charge Controller settings.
![1687953021813.png 1687953021813.png](https://diysolarforum.com/data/attachments/154/154746-289c3cec9f27af81a8911dde6b29760f.jpg)
The Charge Controller MPPT 100 600 seems to have no communication with the BMS. I am surprised there is no setting for Li-on batteries.
![1687953106861.png 1687953106861.png](https://diysolarforum.com/data/attachments/154/154748-ee26f83e421a1a943c43fefbc8aee18d.jpg)
I appologise for the long post, but hopefully some wizard can scan my settings and point out any obvious errors.