Hi guys,

I'm looking for a transfer switch / subpanel combo that provides more than the usual 8 - 12 circuits. I need at least 20 circuits.


Context
  • Currently, we're connecting our PV system to a GenerLink transfer switch which allows us to use all circuits.
  • While not relevant to this thread, it might be nice to know for some of you: the GenerLink is a whole-house transfer switch that is installed between the meter and the service entrance by the utility company. It automatically kicks in once power is supplied from the offgrid PV system (or a gas generator).
  • This is a cool solution, but GenerLink maintenance is up to the local utility company (which isn't very reliable).
  • That's why we'd like to put a redundancy in place.
  • Unfortunately, we can't use an interlock since this nice option isn't permitted in Canada.


Question
  • Can you guys recommend a transfer switch / subpanel combo that sports at least 20 circuits?
  • So far, the most circuits I could find was 12.


Thanks.

James
 
I assume manual transfer, right? The easiest way is interlocked circuit breakers; SquareD sells an interlock that goes between the main and a sub-feed breaker installed on one side. If your generator breaker is <100A then it only takes up two pole spaces so you can have up to 38 extra breaker poles.
 
I assume manual transfer, right? The easiest way is interlocked circuit breakers; SquareD sells an interlock that goes between the main and a sub-feed breaker installed on one side. If your generator breaker is <100A then it only takes up two pole spaces so you can have up to 38 extra breaker poles.
Yes, I'm looking for a manual transfer switch.

Appreciate your input. Unfortunately, I can't get an interlock (see my original post): we're not allowed to use them in Canada (Oh, Canada!).

Have you come across a manual transfer switch that supports at least 20 circuits?
 
here is my manual transfer switch by ABB/GE 100 amps on the lower left
Upper left is the Grid feed incoming into the 6 space 100 amp QO panel. That feeds 1) the transfer switch, 2) the inverter and 3) 30 amp L14-30R

With the transfer switch I can toggle between the Grid and the Inverter, which is further to the right of the picture
the transfer switch feeds the HOMLINE 20 space panel on the right, which is the house critical loads panel

The Grid comes from the original 125 amp panel of the house. The schematic of this system is located on page one of MY BUILD THREAD, referenced in my signature below

20230620_210717.jpg

below is the XW Pro inverter

20230620_210726.jpg
 
  • Unfortunately, we can't use an interlock since this nice option isn't permitted in Canada.

Are all interlocks forbidden, or just the ones mounted on bezel, which are defeated by removal?

Here's one where the interlock remains with the breakers.
It comes with 100A & 30A. I changed to 70 & 70, and output feeds another panel.


If that won't fly, separate transfer switch


There are DIN rail breakers internally interlocked to act as transfer switches. I don't trust the Chinese ones, after buying a "63A" that buzzed at a fraction of that current (maybe misrepresented by seller.) There is a German brand. Get a big enough DIN rail box and you could have what you want.



Those allow very fast snap from one source to the other; determine if you want fast or long dead time.
 
Last edited:
Are all interlocks forbidden, or just the ones mounted on bezel, which are defeated by removal?

Here's one where the interlock remains with the breakers.
It comes with 100A & 30A. I changed to 70 & 70, and output feeds another panel.


If that won't fly, separate transfer switch


There are DIN rail breakers internally interlocked to act as transfer switches. I don't trust the Chinese ones, after buying a "63A" that buzzed at a fraction of that current (maybe misrepresented by seller.) There is a German brand. Get a big enough DIN rail box and you could have what you want.



Those allow very fast snap from one source to the other; determine if you want fast or long dead time.

It might be the restriction applies to the bezel-mounted ones that you can easily remove yourself.

I'll have to look into it.

Thanks for pointing me to the alternatives.
 
Can you run two with 10 circuits transfer/subs? It doubles the cost but likely would pass inspection.
 
i think generac makes an auto transfer with 20 or so circuits that might work with a breaker solution and switch in the middle of the panel. they are about $500 or so.
 
Back