I don’t think it can be done that way. Maybe someone else can chime in on this.Coming out of the main panel to the Grid input of the 18KPV and then back to the main panel from the Load output in the 18kpv to the main panel.
I don’t think it can be done that way. Maybe someone else can chime in on this.Coming out of the main panel to the Grid input of the 18KPV and then back to the main panel from the Load output in the 18kpv to the main panel.
why are you hooking the grid side of the inverter to the main load at all? What you describe is a circular path... what is your overall set up in terms of solar, battery, generator, grid?Coming out of the main panel to the Grid input of the 18KPV and then back to the main panel from the Load output in the 18kpv to the main panel.
why are you hooking the grid side of the inverter to the main load at all? What you describe is a circular path... what is your overall set up in terms of solar, battery, generator, grid?
OK no problem just wasn't sure if I was missing something. But what are the components in your set up? Grid or grid-less, solar or no solar, battery or no battery? If grid, what Amperage is your service? Inverter covering all loads or critical loads? Etc. Would help us to know those
Yes that's the only breaker.Great, that helps a ton. Last question: do you have any breakers upstream from the 200A load box? Like is there a breaker outside on or next to the utility service, that when you flip it cuts all power to the load box? Or is the 200A breaker in the load box the only breaker between meter and you?
I believe you have only two choices given those parameters:
1) you can use a supply side tap which will require the utility turning off the power while you tap into the lines from the meter, see the supply side tap w whole home backup diagram in the manual.
2) You can install a 200A breaker between the meter and the load center which also requires utility to turn off power, and then use a feeder tap that comes off the leg running from the new 200A breaker to the load panel, see feeder tap w whole home backup diagram in manual.
You can't connect to the utility by backfeeding through a breaker in the main panel because that method maxes out at 70A which isn't enough for your whole home backup
That is exactly what I did...except I was lucky in that I had a 200A service disconnect right by my meter, so I didn't have to cut POCO power to hook things up.After reviewing the whole home backup diagram, I have come to realize this inverter is even more sophisticated than I originally thought.
Which is even more than my original motivation to buy it.
So theoretically a person could run some 3/0 directly from the meter to the Grid input of the 18k and then some 3/0 out of the load side of the 18k into the main load panel through it's 200a breaker.
Yes?
One of the things I'm missing for sure.Yes you can connect grid directly into the inverter Grid input and connect inverter Load output directly to the 200A breaker in the load panel. The only problem with this set up compared to using taps/splitters is you cannot easily bypass the inverter in case of an inverter malfunction or failure. The feeder and supply tap diagrams in the manual include a three-way switch that allows you to switch the load panel back to utility power only, bypassing the inverter.
Have you priced double-throw switches lately? Like Justice Potter Stewart once said, “I know obscenity when I see it.”Just need to find a switch that is two position. On-Off-On
That’s not something I would do.But there’s a lot of room in that 18kpv. Could mount a distribution block and save some money.