Question:
Because the T-Fuses are acting fast (which is required here), but how fast is fast? In a server rack filled with 6 EG4 batteries with 100A max. continuous output current it would require a 600A T-fuse at the first look. But what about surge load peaks? I don't know how realistic it is that a surge will pull more than the 600A if a huge inductive load starts. The EG4 batteries can handle surge amps of >102A for 30s and >150A for 3s. The internal short circuit protection in the BMS will trip at >300A per battery in <0.1ms according to documentation.
How should the T-fuse be correctly sized?
Is an additional T-fuse in the rack really necessary or does it make sense if there is a separate 200A battery breaker between the main busbar and each inverter (on top of that, each battery has a it's own 100A mechanical breaker and the BMS as a last resort)?
Because the T-Fuses are acting fast (which is required here), but how fast is fast? In a server rack filled with 6 EG4 batteries with 100A max. continuous output current it would require a 600A T-fuse at the first look. But what about surge load peaks? I don't know how realistic it is that a surge will pull more than the 600A if a huge inductive load starts. The EG4 batteries can handle surge amps of >102A for 30s and >150A for 3s. The internal short circuit protection in the BMS will trip at >300A per battery in <0.1ms according to documentation.