150ah lifepo4 rack battery contender enters Amazon! $1699?

Does it actually have the temp sensors? Can you disable them somehow, maybe using the serial port and their software?
 
Does it actually have the temp sensors? Can you disable them somehow, maybe using the serial port and their software?
It does have temp sensors. 4 total. No software came in the package...I've emailed them.
 

Attachments

  • 20220912_122925.jpg
    20220912_122925.jpg
    123.9 KB · Views: 23
If these work they are by far the cheapest server rack batteries.
 
They just went up another $100. Sucks because I was gonna buy 2 but now I'm just going to wait to see if the EG4s come down.
 
Replacement BMS arrived today (DHL air from CN).

Battery is functioning properly. Tested it with 6kw Inverter running a chop saw and grinder.

Tech support was responsive and helpful. They are sending a 12V 150AH battery at no charge for the inconveniences.

Capacity testing tomorrow....will send update Saturday
 
BMS & status pics...
 

Attachments

  • 20220922_180654.jpg
    20220922_180654.jpg
    80.1 KB · Views: 31
  • 20220922_180657.jpg
    20220922_180657.jpg
    80.7 KB · Views: 15
  • 20220922_180700.jpg
    20220922_180700.jpg
    83.7 KB · Views: 16
  • 20220922_180703.jpg
    20220922_180703.jpg
    83.7 KB · Views: 18
  • 20220922_180718.jpg
    20220922_180718.jpg
    76.3 KB · Views: 31
  • 20220922_180758.jpg
    20220922_180758.jpg
    256.1 KB · Views: 34
  • 20220922_180802.jpg
    20220922_180802.jpg
    358.3 KB · Views: 32
Not operating upon arrival (yet)

Temp sensors not attached

I will report back if/when I get it to come out of protect mode. (3 of 4 temp sensors reading -40c)

Everything looks pretty much identical to what I found in their 300ah 12v battery.
One thing I did find out tonight is that my cells weren't top balanced at all. So may be something to investigate on their Server Rack Batteries as well.

Here's the thread with the details I've found so far.

 
Got mine yesterday and it fired up and ran well, everything in order so far.
However, I could not get it to communicate with anything. I emailed support and got an email from "Pinkie" with software and a manual. Manual is for a different and unknown JBD bms.
Software worked instantly and looks very thorough. It does show the BMS is set to an unusual protocol with no way to change it.

Next 2 posts will show all settings from the factory and a very interesting history log.
 
Parameter NoParameter valuesUnitMinimumMaximumParameter name
0​
0​
0​
0​
1​
1​
1​
16​
RS485 address
11​
16​
1​
32​
Battery node number
12​
15​
mAh
0​
0​
Battery self depletion
13​
0.23​
mO
0​
0​
Sampling resistance
15​
52​
A
0​
0​
Current Limiting Startup
20​
1​
0​
0​
Balance mode
21​
55​
?
0​
0​
Balanced high temperature prohibition
22​
-10​
?
0​
0​
Balanced low temperature prohibition
23​
3400​
mV
0​
0​
Balance starting voltage
24​
50​
mV
0​
0​
Balance starting pressure difference
25​
20​
mV
0​
0​
Balance pressure difference
30​
3550​
mV
0​
0​
Cell high voltage alarm
32​
2700​
mV
0​
0​
Cell low voltage alarm
35​
56000​
mV
0​
0​
Pack voltage high voltage alarm
37​
44000​
mV
0​
0​
Pack voltage low voltage alarm
40​
60​
?
0​
0​
Battery high temperature alarm
41​
0​
?
0​
0​
Battery low temperature alarm
42​
50​
?
0​
0​
Battery charging high temperature alarm
44​
50​
?
0​
0​
Battery discharge high temperature alarm
46​
0​
?
0​
0​
Battery charging low temperature alarm
48​
0​
?
0​
0​
Battery discharge low temperature alarm
51​
60​
?
0​
0​
Environment high temperature alarm
52​
-10​
?
0​
0​
Environment low temperature alarm
53​
90​
?
0​
0​
Power high temperature alarm
55​
105000​
mA
0​
0​
Discharge current alarm
57​
55000​
mA
0​
0​
Charging current alarm
60​
500​
mV
0​
0​
Voltage difference alarm
62​
800​
mV
0​
0​
Voltage difference protection
70​
3650​
mV
0​
0​
Cell over voltage protection
71​
1000​
ms
0​
0​
Cell over voltage delay
72​
3450​
mV
0​
0​
Cell over voltage recovery
73​
2500​
mV
0​
0​
Cell under voltage protection
74​
2000​
ms
0​
0​
Cell under voltage delay
75​
2950​
mV
0​
0​
Cell under pressure recovery
76​
2400​
mV
0​
0​
Cell Shutdown voltage
77​
10​
min
0​
0​
Cell Shutdown time
80​
57600​
mV
0​
0​
Pack over voltage protection
81​
1000​
ms
0​
0​
Pack overvoltage delay
82​
54400​
mV
0​
0​
Pack over voltage recovery
83​
40800​
mV
0​
0​
Pack under voltage protection
84​
2000​
ms
0​
0​
Pack under pressure delay
85​
48000​
mV
0​
0​
Pack under pressure recovery
91​
65​
?
0​
0​
Charging high temperature protection
92​
55​
?
0​
0​
Charging high temperature recovery
93​
-10​
?
0​
0​
Low temperature protection
94​
-1​
?
0​
0​
Low temperature recovery
95​
65​
?
0​
0​
Discharge high temperature protection
96​
60​
?
0​
0​
Discharge high temperature recovery
 
187​
1​
0​
0​
Enable Charge limited current
188​
1​
0​
0​
Enable Pre Charge
189​
0​
0​
0​
Enable Security
200​
1​
0​
0​
Enable Cell-OV
201​
1​
0​
0​
Enable Cell-UV
202​
1​
0​
0​
Enable Pack-OV
203​
1​
0​
0​
Enable Pack-UV
204​
1​
0​
0​
Enable Dsg-OC 1
205​
1​
0​
0​
Enable Chg-OC
206​
1​
0​
0​
Enable Chg-OT
207​
1​
0​
0​
Enable Chg-UT
208​
1​
0​
0​
Enable Dsg-OT
209​
1​
0​
0​
Enable Dsg-UT
210​
1​
0​
0​
Enable Env-OT
211​
1​
0​
0​
Enable Env-UT
212​
1​
0​
0​
Enable FET-OT
213​
1​
0​
0​
Enable FET-UT
230​
1​
0​
0​
Enable Cell-OVP
231​
1​
0​
0​
Enable Cell-UVP
232​
1​
0​
0​
Enable Pack-OVP
233​
1​
0​
0​
Enable Pack-UVP
234​
1​
0​
0​
Enable Dsg-OCP 1
235​
1​
0​
0​
Enable Chg-OCP
236​
1​
0​
0​
Enable Chg-OTP
237​
1​
0​
0​
Enable Chg-UTP
238​
1​
0​
0​
Enable Dsg-OTP
239​
1​
0​
0​
Enable Dsg-UTP
240​
1​
0​
0​
Enable Env-OTP
241​
1​
0​
0​
Enable Env-UTP
242​
1​
0​
0​
Enable FET-OTP
243​
1​
0​
0​
Enable FET-UTP
244​
1​
0​
0​
Enable Dsg-OCP 2
 
TimeModeVoltage(V)Current(A)SOC(%)Residual capacity(Ah)AlarmAlarm informationMinV(mV)MaxV(mV)
2022-09-27 01:54:14Free
52.95​
0​
54​
81.31​
53​
Charging over current alarm recovery04->330805->3312
2022-09-27 01:54:12Charge
53.53​
67.34​
54​
81.29​
37​
Charging over current alarm01->334214->3355
2022-09-27 01:54:12Free
52.9​
0​
54​
81.29​
65​
Charge over current protection04->330505->3308
2022-09-27 01:53:57Free
53​
0​
54​
81.29​
53​
Charging over current alarm recovery02->331205->3315
2022-09-27 01:53:56Charge
53.02​
60.02​
54​
81.28​
25​
Charging over current protection04->331205->3316
2022-09-27 01:53:54Charge
53.58​
60.02​
54​
81.25​
37​
Charging over current alarm01->334514->3358
2022-09-27 01:52:26Free
52.82​
0​
54​
81.14​
53​
Charging over current alarm recovery04->330005->3303
2022-09-27 01:52:24Charge
53.47​
76.34​
54​
81.12​
37​
Charging over current alarm01->333814->3352
2022-09-27 01:26:52Free
52.7​
0​
54​
81.12​
28​
Short circuit protection15->328601->3296
2022-07-13 06:31:56Charge
45​
39.77​
1​
2.9​
52​
Pack under voltage alarm recovery07->280211->2830
2022-07-13 06:31:55Charge
44.96​
39.77​
1​
2.89​
50​
Cell under voltage alarm recovery07->280011->2827
2022-07-13 06:24:59DisCharge
43.75​
39.85​
3​
5.19​
34​
Cell under voltage warning05->269911->2795
2022-07-13 06:24:47DisCharge
44​
39.85​
3​
5.32​
36​
Pack under voltage warning05->271511->2809
2022-07-13 02:41:00Free
54.57​
0​
100​
150.08​
49​
Cell over voltage alarm recovery03->338710->3449
2022-07-13 02:41:00Free
54.57​
0​
100​
150.08​
2​
Cell over voltage recovery03->338710->3449
2022-07-13 02:38:43Free
55​
0​
100​
150.08​
51​
Pack over voltage alarm recovery03->340710->3482
2022-07-13 02:36:45Charge
56.74​
18.04​
99​
149.71​
1​
Cell over voltage protection03->347910->3652
2022-07-13 02:33:58Charge
56.25​
39.81​
98​
147.81​
33​
Cell over voltage alarm03->348002->3551
2022-07-13 02:33:32Charge
56.01​
39.85​
98​
147.66​
35​
Pack over voltage alarm03->347102->3527
2022-07-12 22:10:44Charge
45.04​
49.73​
1​
2.93​
52​
Pack under voltage alarm recovery01->281214->2839
2022-07-12 22:10:40Charge
44.87​
49.73​
1​
2.88​
50​
Cell under voltage alarm recovery01->280214->2828
2022-07-12 21:29:17DisCharge
43.54​
29.93​
2​
3.05​
34​
Cell under voltage warning04->270011->2749
2022-07-12 21:28:54DisCharge
43.99​
29.93​
2​
3.24​
36​
Pack under voltage warning04->273111->2775
2022-07-12 20:36:28Charge
45.08​
29.85​
2​
3.04​
50​
Cell under voltage alarm recovery04->280211->2836
2022-07-12 20:36:25Charge
45​
29.85​
2​
3.01​
52​
Pack under voltage alarm recovery04->279711->2832
2022-07-12 20:28:55DisCharge
43.61​
29.97​
2​
4.22​
34​
Cell under voltage warning04->269911->2769
2022-07-12 20:28:34DisCharge
43.99​
29.97​
2​
4.4​
36​
Pack under voltage warning04->272511->2791
2022-07-12 15:28:28Free
54.62​
0​
100​
149.71​
49​
Cell over voltage alarm recovery03->339010->3449
2022-07-12 15:28:28Free
54.62​
0​
100​
149.71​
2​
Cell over voltage recovery03->339010->3449
2022-07-12 15:27:05Free
55​
0​
100​
149.71​
51​
Pack over voltage alarm recovery03->340810->3479
 
2022-07-12 15:25:42Charge
56.66​
21.68​
100​
150​
1​
Cell over voltage protection03->347310->3652
2022-07-12 15:23:43Charge
56​
29.85​
100​
150​
35​
Pack over voltage alarm03->345910->3558
2022-07-12 15:23:34Charge
55.94​
29.85​
100​
150​
33​
Cell over voltage alarm03->345710->3551
2022-07-12 10:24:39Charge
45.01​
29.81​
33​
50.31​
52​
Pack under voltage alarm recovery04->281014->2829
2022-07-12 10:16:33Free
43.35​
0​
0​
0​
36​
Pack under voltage warning04->270714->2712
2022-07-12 09:56:59Free
44.01​
0​
0​
0​
36​
Pack under voltage warning04->270401->2803
2022-07-12 09:22:23Free
45​
0​
0​
0​
52​
Pack under voltage alarm recovery04->272714->2871
2022-07-12 08:50:24DisCharge
42.86​
30.01​
0​
0​
3​
Cell under voltage protection14->249111->2750
2022-07-12 08:49:28DisCharge
44​
29.97​
0​
0​
36​
Pack under voltage warning14->254011->2808
2022-07-12 08:44:49DisCharge
47.06​
29.97​
0​
0​
34​
Cell under voltage warning14->270011->2980
2022-07-12 00:53:45Charge
53.19​
29.89​
100​
150​
49​
Cell over voltage alarm recovery02->329614->3679
2022-07-12 00:53:45Charge
53.19​
29.89​
100​
150​
2​
Cell over voltage recovery02->329614->3679
2022-07-12 00:53:44Charge
53.3​
29.89​
97​
150​
1​
Cell over voltage protection01->330614->3679
2022-07-12 00:45:42Charge
52.95​
29.89​
91​
138.01​
33​
Cell over voltage alarm01->329214->3550
2022-07-11 23:54:51Charge
46.06​
29.89​
0​
0.56​
50​
Cell under voltage alarm recovery04->280114->3152
2022-07-11 23:54:03Charge
45.01​
29.89​
0​
0.16​
52​
Pack under voltage alarm recovery04->270714->3108
2022-07-11 23:53:43Charge
44.33​
29.81​
0​
0​
4​
Cell under voltage recovery04->263014->3079
2022-07-11 23:48:40DisCharge
42.38​
30.05​
0​
0​
3​
Cell under voltage protection04->245603->2724
2022-07-11 23:47:30DisCharge
43.99​
30.09​
0​
0​
36​
Pack under voltage warning14->258103->2801
2022-07-11 23:44:28DisCharge
46.3​
30.05​
0​
0​
34​
Cell under voltage warning14->269903->2930
2022-07-11 20:55:43Charge
53.91​
29.89​
100​
150​
49​
Cell over voltage alarm recovery01->335014->3635
2022-07-11 20:55:43Charge
53.91​
29.89​
100​
150​
2​
Cell over voltage recovery01->335014->3635
2022-07-11 20:55:42Charge
54​
29.89​
100​
150​
1​
Cell over voltage protection01->335614->3635
2022-07-11 20:51:13Charge
53.52​
28.69​
100​
150​
33​
Cell over voltage alarm01->332814->3564
2022-07-11 20:46:42Charge
53.9​
29.89​
100​
150​
49​
Cell over voltage alarm recovery01->335214->3586
2022-07-11 18:56:09Charge
53.13​
29.89​
86​
129.49​
33​
Cell over voltage alarm01->330314->3551
2022-07-11 18:02:33Charge
46.07​
29.85​
33​
50.53​
50​
Cell under voltage alarm recovery04->280114->3104
2022-07-11 18:01:48Charge
45.02​
29.85​
33​
50.16​
52​
Pack under voltage alarm recovery04->269714->3067
2022-07-11 15:45:27Free
43.76​
0​
33​
50​
36​
Pack under voltage warning04->257214->2834
2022-07-11 15:45:27Free
43.76​
0​
33​
50​
34​
Cell under voltage warning04->257214->2834
 
2022-06-30 14:30:48Charge
53.96​
10.32​
33​
50.01​
53​
Charging over current alarm recovery06->334304->3389
2022-06-30 14:30:47Charge
55.1​
56.18​
33​
50​
37​
Charging over current alarm06->340304->3525
2022-06-27 16:05:01Free
52.83​
0​
100​
150​
49​
Cell over voltage alarm recovery13->329906->3304
2022-06-27 16:05:01Free
52.83​
0​
100​
150​
2​
Cell over voltage recovery13->329906->3304
2022-06-27 16:04:40Charge
53.24​
2​
0​
150​
1​
Cell over voltage protection14->330002->3704
2022-06-27 16:04:35Charge
51.98​
2​
0​
0​
50​
Cell under voltage alarm recovery02->245116->3305
2022-06-27 16:04:35Charge
51.98​
2​
0​
0​
33​
Cell over voltage alarm02->245116->3305
2022-06-27 16:04:34Charge
51.98​
2​
0​
0​
4​
Cell under voltage recovery02->245016->3305
2022-06-27 16:04:21DisCharge
51.99​
2.12​
49​
0​
3​
Cell under voltage protection02->245116->3313
2022-06-27 16:04:13DisCharge
51.98​
2.12​
49​
74.9​
34​
Cell under voltage warning02->245416->3312
2000-00-00 01:53:81Free
52.84​
0​
50​
75​
50​
Cell under voltage alarm recovery01->330206->3304
2000-00-00 01:53:81Free
52.84​
0​
50​
75​
49​
Cell over voltage alarm recovery01->330206->3304
2000-00-00 01:53:80Free
52.83​
0​
50​
75​
34​
Cell under voltage warning09->328210->3324
2000-00-00 01:53:80Free
52.83​
0​
50​
75​
33​
Cell over voltage alarm09->328210->3324
 
Back
Top