Can someone help me with a diagram of 3s2p for solar panels. All panels are 100w

My set up is 12v system.
Renogy Rover Li 40a CC.
1,000w pure sine wave inverter.
Three 120 ah LifePO4 batteries wired in parallel.
 
Last edited:
What is the full spec of the panels, especially the Voc?
What is the maximum PV input Voltage of Renogy SCC?
 
I have two 100w mono Renogy panels and four 100w hqst mono panels

Max input for 12v CC is 550w
 

Attachments

  • Screenshot_20211116-231128.jpg
    Screenshot_20211116-231128.jpg
    176.5 KB · Views: 14
  • IMG_20211116_232145__01.jpg
    IMG_20211116_232145__01.jpg
    119 KB · Views: 14
  • Screenshot_20211116-232556.jpg
    Screenshot_20211116-232556.jpg
    185 KB · Views: 14
Last edited:
OK, the max PV is 100V.
Panel #1 has 24.3V Voc, Imp 4.93A, 5.34A Isc.
Panel #2 has 22.3V Voc, 5.38A Imp, 5.86A Isc.
So you are safe to put 3 panels in series and still be below 100V limit even in cold weather.
The choices will be: the two strings will be connected in parallel.
1) Two strings: each string consists of one Renogy in series with two HQST in series.
2) Two strings: first string consists of two Renogy in series with one HQST, second string will be 3 HQST in series.

Have to do calculation as to which one will produce the most power, I need to do some math.
 
Last edited:
1) Two strings: each string consists of one Renogy in series with two HQST in series.
22.3V + 24.3V x2 = 70.3V
70.3V x 4.93A = 346W per string
2x in parallel = 692W

2) Two strings: first string consists of two Renogy in series with one HQST, second string will be 3 HQST in series.
22.3V x2 + 24.4V = 70V (gets clipped to 66.9V in parallel with other string)
22.3V x3 = 66.9V

66.9V x (4.93A + 5.38A) = 690W

you would never know the difference no matter how you wire them in 3S2P

It’s late…hopefully i did this right…I showed the math!
 
is it better to do 2S3P?
3S2P has the advantage of being very simple to hookup. You just need a pair of MC4 Y-connectors. No extra fusing needs to be done. And the higher voltage will offer a little better low light charging than 2S3P.

2S3P will offer a little better shading performance than 3S2P if arranged properly for the shading patterns. But now you need a combiner box and each of the 3 strings needs to be fused.
 
What about (4s2p) for my setup? Is (4s2p) recommend? It seems like I will be, for lack of a better word, stuck with two panels both facing opposite directions.
 
4S2P could work but given the Voc of the panels you would need a SCC that can handle 120V or more input.

Also keep in mind that all panels in a given series string really should be in the same plane and you want to avoid any partial shading on a series string.
 
I was not so sure if the OP is asking for diagram on how to hook up un-match panel, or just want diagram of 3s2p.
But since OP ask the question I then suspect that OP may not know about the PV Input Voltage limit, that is why I ask about the spec of the panels and the SCC first.
 
I'm going to do the 3s2p. Thank you. Thank you. Very helpful. I will take a pic and show you how my panels are placed on milk crates. I have a flat roof top.
 