I upgraded my charge controller today to an Epever 40 amp controller, and I thought I'd actually ask about proper fuse size because the more I read, the more confused I get. At first I was using a 10 amp PWM controller, 100 watt panel, and a 12 ah SLA battery. I am using 10 gauge wire. I used a 10A fuse on the PV cable and a 30A fuse at the battery. But after doing some searching tonight, I came across something from Renogy that said to use the same size fuse at the battery that the charge controller is rated at. So now that I have a 40A controller I should use a 40A fuse at the battery? Also, the article I read said when fusing from the solar panel to take the amps that the panel puts out, multiply by 1.25, and then round up. A 100 watt panel will output about 5 amps? So 5 x 1.25 = 6.25. Use a 10A fuse at the SCC?
To further complicate things, I came across a thread here where people suggested using the same size fuse from the panel as the SCC is rated for. And the fuse at the battery should be fused according to the wire size. Which I assume a 30A fuse is fine for the 10 gauge I have. But when I get my new 100ah LifePo battery, I plan on going to the max wire size the Epever takes, which is 6 gauge. Then I should step the fuse up?
To further complicate things, I came across a thread here where people suggested using the same size fuse from the panel as the SCC is rated for. And the fuse at the battery should be fused according to the wire size. Which I assume a 30A fuse is fine for the 10 gauge I have. But when I get my new 100ah LifePo battery, I plan on going to the max wire size the Epever takes, which is 6 gauge. Then I should step the fuse up?