Folks,
As we get bigger capacity LiFePO4 cells and then put them in parallel, the internal resistance is going from very small to crazy small.... That means the fault current it getting crazy high. Has anyone seen a good analysis of how to calculate the AIC (Amp Interrupt Capacity) needed for fuses in and around the batteries?
As an example, the internal AC impedance of the Eve 280s is listed as .25mohm. (I did not see a DC Resistance but for this calculation we are talking about a sudden spike in current so AC impedance may be appropriate). Put 8 in series for a 24V system and you get 8*.25 = 2mOhm, but if it is a 2P8S it is 1mOhm. You will have resistance in your bus bars so lets multiply that by 2 to get a pack resistance of 2 mOhm as a first approximation.
At 24v that means the short circuit current is 24/.004=6000Amps. A good class T fuse should handle that just fine. But what about other fuses down stream of the Main fuse?
Does the 10A fuse in the diagram above need an AIC of 6000? What about the 250A fuse?
(If this is covered in another thread, please point me to it)
As we get bigger capacity LiFePO4 cells and then put them in parallel, the internal resistance is going from very small to crazy small.... That means the fault current it getting crazy high. Has anyone seen a good analysis of how to calculate the AIC (Amp Interrupt Capacity) needed for fuses in and around the batteries?
As an example, the internal AC impedance of the Eve 280s is listed as .25mohm. (I did not see a DC Resistance but for this calculation we are talking about a sudden spike in current so AC impedance may be appropriate). Put 8 in series for a 24V system and you get 8*.25 = 2mOhm, but if it is a 2P8S it is 1mOhm. You will have resistance in your bus bars so lets multiply that by 2 to get a pack resistance of 2 mOhm as a first approximation.
At 24v that means the short circuit current is 24/.004=6000Amps. A good class T fuse should handle that just fine. But what about other fuses down stream of the Main fuse?
Does the 10A fuse in the diagram above need an AIC of 6000? What about the 250A fuse?
(If this is covered in another thread, please point me to it)