should be careful of max ratings on these
Not pushing back on your statement, just wanting a broadening of knowledge:
The manual states “190V max PV”
The 161.x Volts is panel specs (135VOC at 77*F) factored for my lowest temperature of -40* which seems ‘safe’ - so at that for worst case I’ll be <85% of label (we had one night of -46*F in 1993, and last winter -39*F but typically -25 to -28*F is lowest. We had -20*F for a week ~2003ish).
So do you think I’m nuts or just mentioning that I’m “too close for comfort” with your sensibilities?
Takeaway: at $85 for these SCC’s if one smokes but doesn’t cause a fire I’m ok with one dying- I have backups.
And if one smokes I may not want to run them anymore anyways. I have a 200V max 50A Epever for primary SCC, and the powrMR will be the second string, and the 1012LV-MK will take 500W, so the setup is redundant as well. Longterm if the 50A 200V Epever doesn’t exhibit the ‘high voltage cutout bug’ with the lithium batteries I’ll probably add a second. Will’s vids and various comments on the forum indicate Epever handles overpaneling fine.
don't have the powMR but my 60A units have 1200W of 2p3s panels on each
I don’t recall if you previously posted what brand SCC? Of course:
24V batteries. Heat is an issue. I have added fans and plenty of clearance but the fans will still run constantly
24V can deal with 1200W input.
I’m 12V lithium so ~13.4V at 60A is ~800W; so my 3S is “945” watts- or 15% overpaneled.
On the voltage, the components are barely rated for the max input. Won't take much of a spike for them to release the smoke. On the conversion side your power will take a big hit at high voltage
2S for me would be ~90VOC and the higher 135 voltage desire is due to ~75 feet one way of run, plus the many cloudy days this time of year where these 315W 2S panels (~92VOC) can often be only ~200Wh/day or less. With other panels, pushing the VOC up gave me as much as two more hours of ‘some’ charge than they did at lower VOC during our months of cloudy days.
If what I’m doing is unsafe (fire hazard) then I’ll rethink it. If it’s just risk of smoking off a $89 SCC- though undesirable- I’ll accept that.
buck converters in these like to operate at 1.5 to 2 times voltage. I'm at about 2.5 times and seeing 80% efficiency. You’re a 12V system(?) so with 160V you're over 10 times differential
Manual states 20-80V “input specification” for 12V systems which I believe is the efficient operating range. Whatever is ‘lost’ is lost as heat, and the highest voltage concern occurs when I am needing heat…
Unless someone provides data of these burning down houses I’m ok carrying on with my experiment.
Peak power is often equal to or better than summer but you just don't have the sunlight hours
Yes. This is my fourth offgrid winter, third full timing it. I’ve seen 600W of 3S2P put out 46A into my lead acid batteries. (Lithium now)
The overpanelled goal is to get >500Wh/day, hoping (aiming?) for 1kWh/day with our cloudy days. My ~2days of storage can be “stretched” to many days with ‘some’ usable input cuz LiFePo won’t die if they do not get fully charged every day.
I’m just trying to know what I don’t know.
don't really see the gains in grabbing a few % in gains from an expensive mppt, when for the same extra cash you can add several more door size panels.
There’s truth to that. But also “it depends” in my mind. If a cheapo mppt is safe to not be likely to cause a fire, more panels, sure. It’s inexpensive- agreed. I like having multiple SCC inputs; multiple ‘good’ SCC expenses can add up, so can panels but not as quickly versus SCC’s for wattage. I’ll accept
some sacrifice of SCC ‘efficiency’ if the cost is reasonably less than buying Victron or something top shelf.