How is feeding solar in the bottom going to increase the load in the main breaker? Feed more power in the bottom and less needs to come in through the main.
Yes, Feeding solar in bottom (or anywhere) decreases load on main breaker.
Of course feeding anywhere but the bottom could result in busbar carrying current equal to Main + PV rating.
First thought is that feeding from bottom, ought to be OK regardless of PV breaker size up to 100% of main, a "200%" rule.
Consider 125A main breaker and 40A PV breaker. 125A flows down one busbar, and 40A flows up from other end, able to feed 165A of loads. Yet, no part of busbar carries more than 125A. Should be OK, right?
Now consider the neutral busbar. If inverters are 240V, not feeding current into neutral, the Line1 busbar has 165A of loads, fed 125A from grid and 40A from inverters. Those 165A of circuits return through neutral wires to neutral busbar, which carries 165A. That is way too much for a 125A busbar!
You might avoid this issue if panel has neutral fanned out to busbars on left and right, and you're careful that Line1 circuits have neutral wires distributed across both (same for Line2). However, the neutral wire from utility is also carrying 165A.
So I now consider the 120% rule important, where I previously thought 200% rule ought to be used.
But, the plans call out the main as 100 amp and label it as new in one place and existing in another. Only saw the existing label the first time though. I also didn't see the stacked full panel and overlooked that the main was in the center.
If 100A main breaker, only 80A continuous or could have nuisance trips. It was noted there were quite a few loads, although I don't know what they add up to.
I don't know if the 120% rule works on a center mounted main.
I understood that 100% was the rule for center mounted. But I've heard that rule got waived in a later NEC?
Knowing this additional info, I think the new 200 amp panel is prob the right decision.
Would be nice to do, 200A (or 225A also commonly available), either 200A or 150A breaker. Square-D has those options, other brands may have others.