With a 40A charge controller you would want 8AWG wire and a 50A fuse between the charge controller and bus bars (or battery). If the Epever has a different output current then size the wire and fuse accordingly.
Ok thank you.With a 40A charge controller you would want 8AWG wire and a 50A fuse between the charge controller and bus bars (or battery). If the Epever has a different output current then size the wire and fuse accordingly.
As I stated in post #12 I wouldn't connect either to the battery terminals.Can you look at the pic of the bank and let me know what terminals you would connect inverter/and controller.
I get that, what I’m trying to say is does it matter which of the positives and which of the negatives I come off of? I know it’s probably a stupid question.As I stated in post #12 I wouldn't connect either to the battery terminals.
That's good, but it doesn't give you any indication of the battery's health. Most worn out lead acid batteries will charge up just fine, the question is: How much energy are they storing? The only way to find that out is to charge it up, then do a load test on it by running a load and measuring the watts being used over time..I separately charges all batteries today. They are all showing good, go up to about 14v and settle at 12.8 to 13.1v. And they hold there.
Perhaps this will help. Download the Wiring Unlimited document:
Wiring Unlimited
Wiring Unlimited is a great resource that covers many many common topics and questions relevant to DIYers. It is a free E-book from Victron Written by Margreet Leeftink. Check it out! Downloaddiysolarforum.com
Go to chapter 3 and look at the section about wiring up parallel batteries. Keep in mind that those diagrams are about single batteries in parallel. Since you have pairs of series batteries in parallel, just replace those single batteries in the diagrams with your series pairs.
Once you go through that you should better understand the diagram you just showed in your last post.
Great, thanks!Perhaps this will help. Download the Wiring Unlimited document:
Wiring Unlimited
Wiring Unlimited is a great resource that covers many many common topics and questions relevant to DIYers. It is a free E-book from Victron Written by Margreet Leeftink. Check it out! Downloaddiysolarforum.com
Go to chapter 3 and look at the section about wiring up parallel batteries. Keep in mind that those diagrams are about single batteries in parallel. Since you have pairs of series batteries in parallel, just replace those single batteries in the diagrams with your series pairs.
Once you go through that you should better understand the diagram you just showed in your last post.
Think I’m just gonna switch them for different batteries.That's good, but it doesn't give you any indication of the battery's health. Most worn out lead acid batteries will charge up just fine, the question is: How much energy are they storing? The only way to find that out is to charge it up, then do a load test on it by running a load and measuring the watts being used over time..
Unless the battery is out of water or has an internal problem, almost all of them will charge up.. but that doesn't tell you how much juice it's holding.
My eyesight is not great but the batteries appear to be the same but have different labels.The batterys are called maintenance free, but they appear to have little slots for a flat head to maybe check fluid.
Think I’m just gonna switch them for different batteries.
This is the list of batteries I will have to choose from….
AGM and Flooded Batteries for SOLAR/RV - general for sale - by dealer
Call: 7-two-0-two-2-four-3-two-1-eight, NO TEXTING or EMAILING Please say Thank You to our VETS. GO NAVY! We sell different Sizes/Types Of AGM and Flooded Batteries, plus Cables, solar controllers,...cosprings.craigslist.org
Which would you suggest?
Have not checked water level.
AGM electrolyte cannot be replenishedAssuming they are all maintenance free then it should not be necessary to check the water levels or specific gravity.
If I'm wrong hopefully someone more knowledgeable on lead acid will correct me.
Ok update , I have 6 12v 149 ah batteries wires to make a 24v bank.If your batteries are 6 volt, and all in series for a 24 volt system the inverter and charge controller wire to the most negative terminal and the most positive terminal.
Im thinking that your dealer is under the impression that you have a 12 volt system.
The batteries i have are hitachi 149ah and they have been working great.None of those batteries are acceptable.. Those are UPS (Uninterruptible power supply) batteries and probably cell tower backup cells. They are not designed for deep discharge and they will not survive in any application that repeatedly discharges them... They're meant to be fully charged and put on a float until the day they're needed when the grid goes down.
You need a true deep cycle battery.. short of that, a golf cart battery would work well enough.. You'd probably get 3 to 5 years from it if you took good care..
Also, unless you have some specific limitation, stay the hell away from AGM batteries.. Good for power sports, good for places where you can't maintain them.. Not so good for life cycle longevity... A flooded lead acid will out last an AGM..
I recommend Trojan SIND line... but that's a serious battery.. Next up would be their SPRE line.. and if the price is too much, get some of their motive T-series batteries like a T105 or T275.
Those look identical to the FLAs for my chassis system. Look at the wide flat-head screwdriver insert in the circles. They're flush-mount caps is allThose look like sealed batteries, confirm?
The interconnects between the batteries look correct and the connections to your loads and charge sources should come off the most positive and most negative terminals.
But...
The wires to the rest of the system are way too small.
I don't see any over-current protection.
No busbars.
No means of disconnect.
And finally no shunt based battery monitor.
The thin wires and lack of over-current protection are safety issues.
The busbars, disconnect and shunt are secondary issues.
I have different batteries now. Hitachi 12v 149ahThose look identical to the FLAs for my chassis system. Look at the wide flat-head screwdriver insert in the circles. They're flush-mount caps is all
This is my issue now…Those look identical to the FLAs for my chassis system. Look at the wide flat-head screwdriver insert in the circles. They're flush-mount caps is all
Draw it on a napkin and take a picture if you have to.
Looks exactly like upnorthandpersonal's drawing. The advice you got here is just fine. Show either drawing to your solar guy. Add numbers to the terminals in the pics. If he tries to say that's not acceptable, I would ask for a concrete reason why and I would ask to speak with someone else in the store, too. Also, let us know what he
His reason was the charge controller will wreak havoc on the inverter. And “how can the batteries charge if your taking a load off them from the same terminals” he said something to that effect.Looks exactly like upnorthandpersonal's drawing. The advice you got here is just fine. Show either drawing to your solar guy. Add numbers to the terminals in the pics. If he tries to say that's not acceptable, I would ask for a concrete reason why and I would ask to speak with someone else in the store, too. Also, let us know what he says.
how can the batteries charge if your taking a load off them from the same terminals
Precisely. He probably found a deal on something he knows enough about to realize a market for. And has learned just enough about to eek by.It sounds like the seller does not understand the parallel circuit but he is still in business selling stuff he does not understand.