Oh I'm a complete noob, I'm not sure what you mean.Thanks @craigcabrey - can you help me understand the conductor current path to clear a N/G fault within the 120v panel of #234?
Oh I'm a complete noob, I'm not sure what you mean.Thanks @craigcabrey - can you help me understand the conductor current path to clear a N/G fault within the 120v panel of #234?
I'm unclear what this complex arrangement is seeking to achieve. Is all this just to alleviate a lost neutral in case of a thermal shut off, or otherwise disconnected autotransformer? Seems like a LOT of parts to potentially fail. If you install an autotransformer and monitor it for a week, it seems to me you'll know the average imbalance and associated heating incurred in normal use. If it goes higher than desired at any point, maybe rebalance the L1/L2 affected loads a little better for that time period to move the higher loads to the other side. And I doubt loads "up the line" are going to affect your installation's neutral current. Not sure you really want to be placing your inverter's neutral in common with the grid's neutral anyway? It would only be the adjacent neighbors using the same small transformer anyway (mine for example has none). I don't plan to have the utility's neutral connected to my house except when the system is bypassed.Okay I overhauled the wiring schematic a bit. In retrospect, I am not confident that designs #133 and #159 would clear ground faults while in on-grid mode. This should resolve that issue, as well as incorporate additional functionalty.
Changelog:
- Adds temp monitoring to AT
- Through K-type thermocouple (continuous measurement) - pictured
- Through OEM switching PTC thermistor (?) - not pictured, optional via NodeMCU ADC
- Ties 120/240V Load Panel neutral permanently to Main Service Panel neutral, eliminating need for G/N bonding contactor (StorEdge wiring method)
- Removes physical cold start push button
- Adds AT neutral current, L1/N, and power factor sensor
- Adds conductor/conduit labels for wiring schematic/BOM
- Changes dry contact signal from 240VAC sensing to 3vDC sensing (logic level)
View attachment 76400
The most important thing this changes is it gives the ability to log sensor data, detect trends, and throw alarms at more conservative values. Since we are now in control of all contactors within the system via software, we can do things like:
Things about this design I'd like to improve:
- Attended, remotely attended (via wifi/internet), or unattended cold start
- Controlling the switchover time of the cold start (how long we want to wait after we stabilize the AT before we allow 120V to our loads panel via the lost N safety contactor)
- Disconnecting power to the AT, the loads panel, or both - contingent on any combination of software-configurable measured conditions, such as:
- Over neutral current
- Power factor
- Over/under voltage
- Over/under temp (either via built-in AT thermistor (?), K-type thermocouple, or both)
- Low voltage (3/5/12VDC Arduino/NodeMCU) components are in the same enclosure as high voltage (120/240VAC) components and may be at risk of EMI
- Thermocouple sensor lines 3.5 and 3.6 are run in the same conduit as L1/L2/N for the AT. Although the sensor cable is shielded, I am not sure if this will affect readings.
- PZEM-004T current sensor has a 1s response time. It's suitable for slower moving trends, but not fast enough to catch over/under voltage conditions (the SVP-912 is 0.1s, in comparison). If we had a sensor with a faster response time, we could get rid of the 2qty SVP-912 devices entirely and control everything with the NodeMCU
Thanks @Cornwallav8r - I'd encourage you to go through the use cases hit on in the pages of this post - I'd suspect you'd arrive at a similar design. There are a lot of details, and there's a reason for every component in the design.I haven't spent as much time studying all the concerns you guys have here that brought you to this point, but this all seems like major overkill.
I'm just a noob here, so I'm really not in a position to provide critical feedback, but I've been following all the comments in this and other other threads and I'm surprised it's crickets now on this one... Could it be you've put this one to rest? Like I said, all this is way above my pay grade, but what you've put together does look very impressive. The only thing I would say, is that the parts list looks like it comes to approx $500, which likely makes a ton of sense with your 3/2 combination.. maybe a little bit less so, with a 1/1 combo.. but then again, you'd be all set to scale up at that point. Congrats again.Here is the build video. I shot this a couple different times and I have found I suck at making good quality videos.
@rfbuehler
Yea, that is on the docket next. I was focused on getting a reliable system that will shut down in the event the neutral is lost. Next up is over temperature protection.
I figured I would post up part's I know for sure will work. That said, you could surely scale back some of the components and save some $$$ for a 1/1 setup. I figure you could probably get this down to 250 dollars if you really wanted to shop.I'm just a noob here, so I'm really not in a position to provide critical feedback, but I've been following all the comments in this and other other threads and I'm surprised it's crickets now on this one... Could it be you've put this one to rest? Like I said, all this is way above my pay grade, but what you've put together does look very impressive. The only thing I would say, is that the parts list looks like it comes to approx $500, which likely makes a ton of sense with your 3/2 combination.. maybe a little bit less so, with a 1/1 combo.. but then again, you'd be all set to scale up at that point. Congrats again.
John
I am a complete novice here, but let me ask a question. If you have 2 Transformers instead of one, and your 120 V loads aren't that high, wouldn't that provide a safety backup if one of them failed?I figured I would post up part's I know for sure will work. That said, you could surely scale back some of the components and save some $$$ for a 1/1 setup. I figure you could probably get this down to 250 dollars if you really wanted to shop.
We still need to add in temp monitoring and it would also be awesome to add on a genset switch to this setup - so everyone gets their end state and could see what a "fully loaded" setup looks like.
Redundancy is the most important step someone can take in this setup IMO. I however don't want to leave things to chance, I have too much to lose to be cheap on that part of the setup.I am a complete novice here, but let me ask a question. If you have 2 Transformers instead of one, and your 120 V loads aren't that high, wouldn't that provide a safety backup if one of them failed?
Do the inverters themselves not have a breaker on the bottom of them? Is that not what that breaker already does?I finally got the time to actually look at your circuit and watch your video. One thing I'd add other than the temp protection on the transformers is I would add (3) breakers between your inverters and where you join their outputs. In this circuit there is no overload protection on the inverters and wiring coming from the inverters.
Other than that everything looks good.
I was looking at the Victron AT and thinking it may have actually been a better choice to begin with for my setup. A little late now LOL.Sorry, I’m being the devils advocate on your protection. Victron’s Autotransformer has one feature that could be added here. There have a high temp trip that trips the output on high temp. You could add a temp relay and use the temp sensor already in the Autotransformer and trip the shut breaker on high temp. It’s a pre-emptive trip. Trip before there is a problem. If you want to go a step further you could add a pi to do some monitoring so that if you do have a trip you know what caused it. (Easier to fix if you know the SOE) A SOE recorder is overkill.
Are you thinking just using the Victron in lieu of your entire set up will solve the issues with grid connection and AT failure?I was looking at the Victron AT and thinking it may have actually been a better choice to begin with for my setup. A little late now LOL.
I am not sure, but it looks like a much more substantial unitAre you thinking just using the Victron in lieu of your entire set up will solve the issues with grid connection and AT failure?
I like your protective circuit a lot. How would you modify it for 4 inverters? That doesn't look like it would be easy to do.Redundancy is the most important step someone can take in this setup IMO. I however don't want to leave things to chance, I have too much to lose to be cheap on that part of the setup.
Sure it would. You have a couple methods to do it, easiest method being to get a 4 pole contactor. Just make sure the breakers and wiring is sized appropriately for your workload.I like your protective circuit a lot. How would you modify it for 4 inverters? That doesn't look like it would be easy to do.