My understanding is he disconnected the AC input from the main panel. The small panel supplied by the inverter is still connected.
Maybe I'm reading wrong but that was my take on the situation.
That is what my thinking is, if the bonded small panel is connected to AC output which I understand to be the case. If the small panel is connected and bonded and the inverter is bonding N-G, then he has 2 bonds.
Again, my understanding is the small panel is connected.
I'd rather determine what is connected and disconnected before moving on to a solution. I'd prefer an earth reference no matter what with an EGC from the service panel to the inverter connected.
You have a good point there.![]()
I have no AC input. Just "for now" only have 8 36v panels (280w), EG4 3kW 120V inverter and two 5kW lithium batteries.
According to tech at SigSolar he told me after I did continuity test over phone with him the neutral & bond were connected in AIO.
When I first checked inverter with battery on, but AIO in off position there was no continuity. After turning the AIO on, I got continuity.
There is a note in manual that says "When the inverter is working in PV mode, battery mode or standby mode, the output neutral is connected to the ground of AC output (neutral/ground bonded).
When the inverter is working in AC mode, neutral of output is disconnected to grounding of AC output and connected to neutral of AC input."
See attached pic.
My understanding from phone call the bonding "somehow discoonects" when connected to AC input