My system is 2kW feeding two series Battleborn's for a 24v-100ah storage.
I'll be installing a Multiplus Compact 24-2000 (2000-50a) inverter/charger
Now that part I've become more and more confused about is the grounding of the entire system- both AC portion and DC portion.
I assume this parts correct- the AC portion is grounded through the AC junction boxes with the ground wire going back to the MAINS panel.
If that's incorrect- tell me how to correct it (not theoretical- practical).
Here's what Victron says;
This is a Safety Class I product (supplied with a protective grounding terminal). Uninterruptible protective grounding must be provided at the AC input and/or output teminals and/or chassis grounding point located externally on the product.
So here comes the harder part- the DC grounding- no idea what I'm supposed to do.
The Multiplus manual says;
Ground relay (see appendix B) With this relay (H), the neutral conductor of the AC output is grounded to the chassis when the back-feed safety relay is open. This ensures the correct operation of earth leakage circuit breakers in the output. If a non-grounded output is required during inverter operation, this function must be turned off. (See also Section 4.5) Not adjustable with DIP switches.
This is a Safety Class I product (supplied with a protective grounding terminal). Uninterruptible protective grounding must be provided at the AC input and/or output terminals. Alternatively the grounding point located externally on the product may be used. Whenever it is likely that the grounding protection has been damaged, the product must be turned off and secured against unintended operation; please contact qualified
service staff.
Another problem is that of DC grounding of my system. Yes, I know the panels don't get grounded. How about some sort of ground rod with the BMV-712 attached to it with a cable?
I've read and have tried to understand Victron's wiring manual but haven't learned too much.
Looking for help....
Thanks
P.S. Have seen way too many youtube videos about the subject. I suppose it's a liability issue- wrong advice and God only knows you can get sued.
I'll be installing a Multiplus Compact 24-2000 (2000-50a) inverter/charger
Now that part I've become more and more confused about is the grounding of the entire system- both AC portion and DC portion.
I assume this parts correct- the AC portion is grounded through the AC junction boxes with the ground wire going back to the MAINS panel.
If that's incorrect- tell me how to correct it (not theoretical- practical).
Here's what Victron says;
This is a Safety Class I product (supplied with a protective grounding terminal). Uninterruptible protective grounding must be provided at the AC input and/or output teminals and/or chassis grounding point located externally on the product.
So here comes the harder part- the DC grounding- no idea what I'm supposed to do.
The Multiplus manual says;
Ground relay (see appendix B) With this relay (H), the neutral conductor of the AC output is grounded to the chassis when the back-feed safety relay is open. This ensures the correct operation of earth leakage circuit breakers in the output. If a non-grounded output is required during inverter operation, this function must be turned off. (See also Section 4.5) Not adjustable with DIP switches.
This is a Safety Class I product (supplied with a protective grounding terminal). Uninterruptible protective grounding must be provided at the AC input and/or output terminals. Alternatively the grounding point located externally on the product may be used. Whenever it is likely that the grounding protection has been damaged, the product must be turned off and secured against unintended operation; please contact qualified
service staff.
Another problem is that of DC grounding of my system. Yes, I know the panels don't get grounded. How about some sort of ground rod with the BMV-712 attached to it with a cable?
I've read and have tried to understand Victron's wiring manual but haven't learned too much.
Looking for help....
Thanks
P.S. Have seen way too many youtube videos about the subject. I suppose it's a liability issue- wrong advice and God only knows you can get sued.