No, the problem persists .Have you sorted this?
It could be your string voltage exceeding 450V and the MPPT shutting down.
Rewire your series string so that you do not exceed 450V max power volts, the ratings are usually on the nameplate of the panel.
I have considered that I was putting in too much voltage as there are 2x strings of 14 x 400 watt panels, @ 5600w, and thought this might cause a shutdown as takes it just over the SPF capacity of 5000w ?
I can easily take out panels from the strings but will this stop the shutdowns ?
Last week I did take out 2x panels from one string but it shut down when batteries were full , again .
Maybe I,ll take out 4x panels from each string , so 4000w input , this could prove the theory ?
I am running on AGM battery settings ,if I try to set on Li type , warnings start of low voltage on both inverters ,
and no charge goes in ,
I can,t seem to win !
Today I fitted isolator switches to be able to turn the panels off without going over to the array combiner boxes , (30 metres away )
and when removing one of the MC 4 connectors fitted at the end of the 30 metre run from the panels , saw that it had partially melted !!
All replaced now but what would cause that ?