ADDvanced
New Member
- Joined
- Sep 6, 2022
- Messages
- 133
Shed System: 2x200AH AmpereTime Lithiums, 3x 240W 24v solar panels, & a renogy rover 60A MPPT charger, small 400w inverter.
I am currently living in a shorty school bus with a smaller solar system (2x100w panels, 20a MPPT charger, 2x100Ah AGMs).
The weather has been bad, snowing for 3 days with no sun, so the power was running low on the bus. The shed was at 100% power, because i have 3 24v panels wired in series so even on overcast days, it manages to keep the power up to 100%. Anyway, last night, the bus was running low on power, so I turned the inverter on in the shed, and ran an extension cord to the bus, and put a battery charger on the bus batteries. This worked great.... except it was new years, celebrations were happening, and I passed out and left it plugged in.
Cue to this morning. Wifi is down (in the shed). Go out to the shed, and the Rover MPPT charger display is showing the batteries are at 0%, and are showing 5 volts. What do I do? I tried flipping it around, and putting a battery charger on the ampere time/lithium batteries to see if I could wake them up so the solar could start charging them, but I watched as the voltage went DOWN when I hooked up the charger
Okay, update, I disconnected the batteries from everything and checked with a meter, they are showing 11.4V.... where do I go from here? 11.4V should be high enough to charge, but the Renogy Rover was showing 0% SOC. ??? Very confused this system has been working fine for months.
I am currently living in a shorty school bus with a smaller solar system (2x100w panels, 20a MPPT charger, 2x100Ah AGMs).
The weather has been bad, snowing for 3 days with no sun, so the power was running low on the bus. The shed was at 100% power, because i have 3 24v panels wired in series so even on overcast days, it manages to keep the power up to 100%. Anyway, last night, the bus was running low on power, so I turned the inverter on in the shed, and ran an extension cord to the bus, and put a battery charger on the bus batteries. This worked great.... except it was new years, celebrations were happening, and I passed out and left it plugged in.
Cue to this morning. Wifi is down (in the shed). Go out to the shed, and the Rover MPPT charger display is showing the batteries are at 0%, and are showing 5 volts. What do I do? I tried flipping it around, and putting a battery charger on the ampere time/lithium batteries to see if I could wake them up so the solar could start charging them, but I watched as the voltage went DOWN when I hooked up the charger
Okay, update, I disconnected the batteries from everything and checked with a meter, they are showing 11.4V.... where do I go from here? 11.4V should be high enough to charge, but the Renogy Rover was showing 0% SOC. ??? Very confused this system has been working fine for months.