Hello everyone!
I hope you are all doing well. I am responsible of some solar projects, mainly from the electrical side of things, plus connecting batteries, BMS and programming, based on what is required. Usually, these work just fine, and the projects are all possible to do and are always met with success with the client being satisfied.
Today, however, I was tasked with something that I truly never came across before, as a demand anyway. Their system is composed of:
- SUN-8K-SG01LP1 DEYE inverter
- 8400 Watt solar panels (using the double MPPT of the inverter)
- 2x 200Ah GreenSun Solar LiFePo4 Batteries (in parallel. NOTE: Those are 1P15S LiFePo4, NOT 1P16S!)
Connections wise, including BMS communication using CAN protocol were all successful. So no problems there.
The problems arise with what the client wants on their "SUN-8K-SG01LP1" inverter (that seemed out of the normal):
1- The possibility to be able to draw out some 25-30 Amps from the batteries alone, or at the very least some 15 Amps on 230V. That's the equivalent of anything between 80-170 Ah on the batteries. I asked to make sure, and indeed they want to have the possibility to be able to empty the batteries in 2 hours if necessary.
2- They want a scheduling system that pretty much acts like a Hysteresis for the LiFePo4. For example, they want to draw only from the batteries even when utility is present (it's connected on the "GRID" side, not the "GEN" side as the frequency is not really stable), and as soon as it reaches a certain set point (say 20% SOC at night), the utility is to slowly charge the batteries back up to another certain set point (say 60%) until morning, where the solar will take over.
3- They want the ability to set a limit to the pull current (internally, not externally with a current limiter, etc.) from the utility, so that they can divide the load between utility and batteries. Yes, utility + batteries, not just Solar + Utility (with priority to Solar), nor Solar + Batteries, but utility + batteries. In other words, they want to set a certain amount of current (say 8 Amps) to draw from the utility, and the rest from the batteries.
To be completely honest, this is the first time I've seen such demands. Usually, I've seen that second option somewhat possible on inverters like Growatt, Blue Sun, Snaterm, Jesudom, Anern, Voltronic, Sako, MUST, etc., where you have the option to switch back from SUB to SBU as soon as the battery charging reaches a certain voltage. But even then, it only applied for Lead-Acid Tall Tubular, AGM or Gel batteries, and LiFePo4 ONLY IF BMS is disabled (user-defined battery settings). I didn't see DEYE having such a feature, to be honest.
For the first demand, we did a bit of testing when the batteries were around 60% SOC, and they began to add more and more load (at first still not realizing that they actually want that high a consumption/load), and when it reached some 80 Amps consumption on the batteries, the voltage had already dropped by more than 2 Volts, going below 47V threshold, which triggered an alarm on the inverter and immediately cut the power off the loads. (KINDLY REMEMBER, these are 15S cells LiFePo4, not 16S, so the max possible voltage to charge them with is actually 54.4V, not 57.6V, so voltages in the high 40s is normal. The batteries were displaying it on their own screens). I thought about it, and the only solution I could find is to go into "Advanced" mode, where I basically remove the BMS and focus solely on the voltage, and based on my calculations, apply the proper Bulk and Floating voltages (which are very close to each other), and a cut-off voltage that is the equivalent of around 20% of the batteries' SOC. I proposed it, but he refused to remove the BMS. Personally though, I'm against the idea of drawing that much power simultaneously.
As for their third demand, I tried checking if I could trick the scheduler in some way to at least stop the consumption from the batteries and switch to batteries instead, but no dice. It was just conflicting with the regular charging process which was set in the "Battery Settings", and simply refused to charge them until I disabled the scheduling altogether.
So, what do you guys think? What is the action that I should take? I can clearly see that there are many security risks as it is, especially on the batteries as they would have a significantly shorter life because of that heavy draw (among many other things), but hey, that's what they want.
Oh, and this is the battery they've bought (two of them):
Thank you all in advance, and sorry for the long thread!
I hope you are all doing well. I am responsible of some solar projects, mainly from the electrical side of things, plus connecting batteries, BMS and programming, based on what is required. Usually, these work just fine, and the projects are all possible to do and are always met with success with the client being satisfied.
Today, however, I was tasked with something that I truly never came across before, as a demand anyway. Their system is composed of:
- SUN-8K-SG01LP1 DEYE inverter
- 8400 Watt solar panels (using the double MPPT of the inverter)
- 2x 200Ah GreenSun Solar LiFePo4 Batteries (in parallel. NOTE: Those are 1P15S LiFePo4, NOT 1P16S!)
Connections wise, including BMS communication using CAN protocol were all successful. So no problems there.
The problems arise with what the client wants on their "SUN-8K-SG01LP1" inverter (that seemed out of the normal):
1- The possibility to be able to draw out some 25-30 Amps from the batteries alone, or at the very least some 15 Amps on 230V. That's the equivalent of anything between 80-170 Ah on the batteries. I asked to make sure, and indeed they want to have the possibility to be able to empty the batteries in 2 hours if necessary.
2- They want a scheduling system that pretty much acts like a Hysteresis for the LiFePo4. For example, they want to draw only from the batteries even when utility is present (it's connected on the "GRID" side, not the "GEN" side as the frequency is not really stable), and as soon as it reaches a certain set point (say 20% SOC at night), the utility is to slowly charge the batteries back up to another certain set point (say 60%) until morning, where the solar will take over.
3- They want the ability to set a limit to the pull current (internally, not externally with a current limiter, etc.) from the utility, so that they can divide the load between utility and batteries. Yes, utility + batteries, not just Solar + Utility (with priority to Solar), nor Solar + Batteries, but utility + batteries. In other words, they want to set a certain amount of current (say 8 Amps) to draw from the utility, and the rest from the batteries.
To be completely honest, this is the first time I've seen such demands. Usually, I've seen that second option somewhat possible on inverters like Growatt, Blue Sun, Snaterm, Jesudom, Anern, Voltronic, Sako, MUST, etc., where you have the option to switch back from SUB to SBU as soon as the battery charging reaches a certain voltage. But even then, it only applied for Lead-Acid Tall Tubular, AGM or Gel batteries, and LiFePo4 ONLY IF BMS is disabled (user-defined battery settings). I didn't see DEYE having such a feature, to be honest.
For the first demand, we did a bit of testing when the batteries were around 60% SOC, and they began to add more and more load (at first still not realizing that they actually want that high a consumption/load), and when it reached some 80 Amps consumption on the batteries, the voltage had already dropped by more than 2 Volts, going below 47V threshold, which triggered an alarm on the inverter and immediately cut the power off the loads. (KINDLY REMEMBER, these are 15S cells LiFePo4, not 16S, so the max possible voltage to charge them with is actually 54.4V, not 57.6V, so voltages in the high 40s is normal. The batteries were displaying it on their own screens). I thought about it, and the only solution I could find is to go into "Advanced" mode, where I basically remove the BMS and focus solely on the voltage, and based on my calculations, apply the proper Bulk and Floating voltages (which are very close to each other), and a cut-off voltage that is the equivalent of around 20% of the batteries' SOC. I proposed it, but he refused to remove the BMS. Personally though, I'm against the idea of drawing that much power simultaneously.
As for their third demand, I tried checking if I could trick the scheduler in some way to at least stop the consumption from the batteries and switch to batteries instead, but no dice. It was just conflicting with the regular charging process which was set in the "Battery Settings", and simply refused to charge them until I disabled the scheduling altogether.
So, what do you guys think? What is the action that I should take? I can clearly see that there are many security risks as it is, especially on the batteries as they would have a significantly shorter life because of that heavy draw (among many other things), but hey, that's what they want.
Oh, and this is the battery they've bought (two of them):
Thank you all in advance, and sorry for the long thread!