"conforms to", I (think) is not the same as certified by NRTL.
The link appears updated, now says, "UL Standard 1640 / Certified to CAN/CSA Std. C22.2 #14."
"inspect us regularly" which is part of the process to maintain listing.
I expected "listed", not "conforms to" which suggests in-house design goals, not the highly stressing tests used for certification.
I was in particular mocking the "UL Approved" I have seen, which I took to be a counterfeit label because AFAIK UL does not "Approve" anything, only "Lists".
You may have a listing document for your product. If so, can you link to that? I think it would have listing numbers for that product which customers could verify and the agency's site.
"Break before make" is certainly what you want.
But if you HyPotted it, what voltage could it hold off?
Consider this Carling breaker:
"Dielectric Strength 1960 VAC, 50/60 Hz for one minute between all electrically isolated terminals, except 2500 VAC for one minute between alarm/aux. switch and main terminals with contacts in open and closed position. F-Series circuit breakers
comply with the 8mm spacing & 3750VAC 50/60 Hz dielectric requirements from hazardous voltage to operator accessible surfaces, between adjacent poles and from main circuits to auxiliary circuits per Publications EN 60950 and VDE 0805"
I'm presently using UL listed interlocked QO breakers for my transfer switches. Don't want to risk having grid backfeed my inverters, or vice versa.
The rocker switch you used may in fact be UL listed or equivalent. For some application.
My concern was that it might not meet the requirements to isolate generator from grid. Which may be different from "operator accessible" of the above link. (or not, since grid is accessible to lineman during repairs?)
A complete product intended to serve as generator transfer switch ought to be tested and listed to the requirements of the application.
If your product is compliant, then My Apologies! Please provide documentation that it is listed to UL requirements.
trust me we know transfer switches completely!
I will admit I do not, and I am not a licensed PE. Just an EE who pokes his nose into things.
"UL Standard 1640" is for portable equipment?
That, I think, would be applicable to the portable generator.
But is your product supposed to be permanently installed in house, hard-wired to the grid? e.g. as a transfer switch to feed furnace from generator vs. grid?
Here's a page from Schneider on transfer switches. No mention of 1640, but some others:
Manual transfer switches are used in backup power systems that serve loads classified as optional by the NEC®.
www.ascopower.com