I searched and can't find the answer, even though I'm sure it's probably been answered a million times.
I bought a smartsolar 150/45 and I guess I need to know what the overpanel limits are.
The specs for it say 150v input max and 50a input current, which leads me to calculate 7500w max panels but obviously the specs don't agree and say it's limited to 2600w at 48v.
Curious
I live in Oregon and need max performance in low light and cloudy conditions so I want to overpanel as much as I can.
Is it ok to connect 8x 440w panels in 2s4p which adds up to 3200w max? 49.5voc 10.5a isc per panel which equals around 100v 42a?
Am I right to assume there's no way it can do 9x 440w panels in 3s3p, even if I add long leads to intentionally add voltage drop, that the voltage could still exceed max in cold conditions?
I bought a smartsolar 150/45 and I guess I need to know what the overpanel limits are.
The specs for it say 150v input max and 50a input current, which leads me to calculate 7500w max panels but obviously the specs don't agree and say it's limited to 2600w at 48v.
Curious
I live in Oregon and need max performance in low light and cloudy conditions so I want to overpanel as much as I can.
Is it ok to connect 8x 440w panels in 2s4p which adds up to 3200w max? 49.5voc 10.5a isc per panel which equals around 100v 42a?
Am I right to assume there's no way it can do 9x 440w panels in 3s3p, even if I add long leads to intentionally add voltage drop, that the voltage could still exceed max in cold conditions?