We are in total agreement on this.Not possible to have 25A flow in L1 and 25A flows out of center-tap N, while 0A flows through L2. Inductance doesn't allow it.
We are in total agreement on this.Not possible to have 25A flow in L1 and 25A flows out of center-tap N, while 0A flows through L2. Inductance doesn't allow it.
I disagree. You put 12.5A in L1 of an auto-transformer. That flows and supplies 12.5A to center tap N of transformer and load.
Magnetic coupling sucks another 12.5A in L2 of auto-transformer (note I said "in", not "out", at any given instant it is flowing in opposite direction not same direction as current in L1), and supplies a second 12.5A for 25A in N.
The key here is to think in terms of current which is not "in phase" as you like to say about split-phase systems, but rather current at 0 degrees phase or 180 degrees phase. Same direction or opposite direction.
There is never 25A flowing in L1 and out L2. It is one big inductor, can't get more than a fraction of an amp to flow at 60 Hz. The only way to have 25A flow in L1 is to have 25A flow in L2. They are flowing in opposite directions. When the meet in the middle, they both flow out N for 50A. And that is 2x the transformer's rating.
12.5A I say it is.
This is NOT an isolation transformer, where current flowing in secondary allows current to flow in L1, out L2.
Just split-phase in general. Because people think that it's two phases 180 degrees out of phase with each other.Did you post this regarding breakers in a split-phase panel, possibly MWBC? Or regarding auto-transformer?
AbsolutelyIn an auto-transformer, only low (magnetization?) current flows from L1 to L2. Whatever inductance allows.
With a 120V load between N and one of the two Ln, current flows from L1 to N and into the load, and simultaneously flows from L2 to N (swimming upstream) and into the load. When polarity of AC voltage reverses, current flows from load and then from N to L1, and same/similar amount of current flows from load and then from N to L2.
Kirchhoff's current LAW holds true. Two coupled windings and the center tap N join at a node. Sum of currents into that node is always zero. If 25A flows out of N, then 12.5A flows into L1 and 12.5A flows into L2.
I've demonstrated this on the bench. Cmiller is going to replicate or refute my results. You previously refuted them, but I need to see your no-load current (center tap N disconnected from load) to see if you just had a very non-ideal transformer and too light a load.
I think we will all agree about Kirchhoff's current law. Exact values of L1, L2, N current will vary. The fundamental behavior of coupled windings is what I have been arguing about.
This is why the Victron Autotransformer has a solenoid trip for its main breaker based on toroid temperature, not Neutral current.Like a motor winding, it has some thermal mass and takes a bit of time to warm up. So motor-rated breakers that allow a half to a few seconds of moderate overload should be fine.
Correct. The issue lies in a power outage scenario. I don't believe that it is best practice to have more passthrough loads than what an inverter can handle during a grid outage. You run the risk then, of having a complete power failure when grid is down, due to inverter overload. Kinda defeats the whole point of a "hybrid" inverter with batteries.If using the pass through, it can be as much as 200a.
You are right that it depends on what you feed it from. I would put money on it, that the average double or triple 15k install does NOT have more than a 200A electric service to start with. So then you may as well only run 100A through each inverter... and in the downstream panel you won't want more than 200A anyway, unless you are splitting to 2 panels.It just depends on what you feed it from.
You could limit the input with a reduced feed.
And this could keep you from overloading the panel.
If I had an issue with an inspector, I would bring up the NEC articles on how to size breakers for PV inverters. (Rated output x 1.25 and round up to nearest breaker size.) Sorry I don't know where it's found offhand. Don't have my code book in front of me. That would make the relevant breaker size for a 15k an 80A. (62.5 x 1.25 (78A) == 80A breaker)Every situation is different. And anything can be made to work.
I'm not saying that you can't make it work. I'm saying that I wouldn't recommend doing it that way. And passing inspection with it has been difficult for people.
Because there are no provisions in the NEC for it. So, most inspectors don't accept it. If you are not getting it inspected, then you can of course do whatever you want. It can be done safely.
We are in total agreement on this.
This is why the Victron Autotransformer has a solenoid trip for its main breaker based on toroid temperature, not Neutral current.
Short excessive unbalances over 30A do not trip it. They claim 28A continuous depending on ambient temp.
Never mind! $120 is actually not awful at Gordon.Bad news: at $256 msrp It costs about as much as the Growatt autotransformer.
We agree that the 120v loads current inside the autotransformer is divided in half on the 240v feeding the autotransformer.
Were we disagree on the feed breaker size, is on how the actual loads will be presented to the breaker.
I say that it depends on how the autotransformer is connected.
In line with the feeder, I say protect the feeder. (As it will be carrying the most current)
Or "T" tapped at the loads, I say protect the neutral. (As it will be carrying the most current)
You say protect at the neutrals rating in both cases.
Never mind! $120 is actually not awful at Gordon.
When I first got started in 2019-20 buying stuff and watching Wills early videos , I didn’t have a clue what I needed to buy… . so I bought all Victron .BB and Blue Seas stuff as he was into that stuff at that point..Exactly the problem I face here in Puerto Rico. Ive called multiple electricians and as soon as i say offgrid or solar theyre turning their backs on me. This Forum has been the BEST source to fix my problem. This is my very first time posting or reading from a Forum and its been an amazing experience.
Yep. Lol. This is the direction I was starting to think.Maybe the difference is circuit topology.
I've been saying 12.5A 2-pole breaker feeding autotransformer + loads was necessary to protect it. (e.g. only the 2-pole breaker on left of this drawing.) that's upstream breaker.
What I just realized is, if we feed the autotransformer only with 240V from source, then daisy chain off its L1/L2 to a sub-panel with backfed 25A transformer, and also connect centertap of transformer neutral bus of that panel, then autotransformer is protected. Current drawn from that panel will always have |N| = |L1 - L2|, Neither L1 nor L2 can exceed 25A so N can't exceed 25A. That allows loads to be 25A 120V on L1, or 25A 120V on L2, or 25A 240V on L1 & L2. that's downstream breaker.
While it doesn't let you run loads willy-nilly like the Victron transformer with 100A pass-through breaker, it is probably good enough for most DIY work.
View attachment 208294
This is were I was. Because of how the Growatt autotransformer is wired. Input and output, instead of "T" tapped at the loads panel.Maybe the difference is circuit topology.
I've been saying 12.5A 2-pole breaker feeding autotransformer + loads was necessary to protect it. (e.g. only the 2-pole breaker on left of this drawing.) that's upstream breaker.
What I just realized is, if we feed the autotransformer only with 240V from source, then daisy chain off its L1/L2 to a sub-panel with backfed 25A transformer, and also connect centertap of transformer to neutral bus of that panel, then autotransformer is protected. Current drawn from that panel will always have |N| = |L1 - L2|, Neither L1 nor L2 can exceed 25A so N can't exceed 25A. That allows loads to be 25A 120V on L1, or 25A 120V on L2, or 25A 240V on L1 & L2. that's downstream breaker.
While it doesn't let you run loads willy-nilly like the Victron transformer with 100A pass-through breaker, it is probably good enough for most DIY work.
View attachment 208294
That’s fine? I’m confused, in his drawing he has L2 going into neutral busbar. In my set up I have L2 going into a 30a breaker which feeds phase 2 on my left panel.That's fine,
Except that the grey wire in the drawing, between the inverters and transformer, should be black. So that it's not confused with a neutral.
Moot point, since slash breakers wont fit in a high leg panel...I think the comments laid it out pretty clearly. But commenters aren't authoritative, just as we forum members aren't.
"I've heard them called "slash rated". The lower rating is phase to ground voltage, the higher is phase to phase. As Bird dog said, the issue comes up in wanting to use the high leg on a 3P4W delta for a single phase 208v load; the breaker has to have a phase to ground rating of at least 208v, which a slash rated breaker does not."
"120/240V Slash rated breakers are suitable for 1Φ or 3Φ loadcenters, where the highest voltage to ground is 120V and the max voltage phase to phase is 240V. Also used in 120/208V 3Φ 4W Wye systems.
240V Straight rated breakers are suitable for 1Φ or 3Φ loadcenters, where the highest voltage to ground is 240V and the max voltage phase to phase is 240V. Such as in a Center tapped delta system, where the wild leg is 208V to ground.
Most 3P breakers come standard with a straight 240V rating.
2P units can come either way, normally slash rated, but straight rating is required if your connecting to a 208V wild leg.
BR240H is an example of a 2P unit with a straight rating, for use on a center tapped delta system."
Good catch.That’s fine? I’m confused, in his drawing he has L2 going into neutral busbar. In my set up I have L2 going into a 30a breaker which feeds phase 2 on my left panel.
Did I do something wrong?
Moot point, since slash breakers wont fit in a high leg panel...
I don't know either.What is a "high leg panel"?
How is it different from any QO 3-phase panel?
What is a "high leg panel"?
How is it different from any QO 3-phase panel?