Modbus comms with (Deye) inverter

I tried pin 7, 8 and also 1,2 but without any results with read function, You mean pin 3, 4?
 
Cheers,

@festr, lets try study modbus map from me, which I obtain directly from deye support. The datasheet was tranlated by deepL. Modbus map is for 3phase Hybrid LV inverters, but maybe usable for HV models.

Others: Maximum sell power is possible driving by register 340 on 3phase Hybrid. But I don't know, if you do some massive writes into inverter and the FLASH memory will be happy next year.

Have anyone some information about massive Modbus writes and impact to lifetime? Maybe storage is RAM with capacitor or battery backup, then it is right. Otherwise I will be scared.
 

Attachments

  • from DEYE SG04LPxx MODBUS RTU-V102 en-US.pdf
    923 KB · Views: 96
@HonzaS Thanks!
Too bad REG 141 description is a total mess. I think it represents System Work mode.
I'd be interested switching between Zero Export to Load and Zero Export to CT by modbus command.
 
Found it and verified regWrite() with Deye Cloud Read of System Work Mode-1 Page for 12k 3f model.
System Work Mode = REG 142
0 : Solar Sell
1: Zero Export to Load
2: Zero Export to Ct
 
Hello,

I have the same problem as you because modbus table from Deye is in bad English translation.
I bought this RS 485 converter and with help from my colleague who understands modbus better then me we find some useful data.
Converter: USR-TCP232-410s RS232 / RS485 Serial to Ethernet Adapter/IP Device Server Ethernet Converter Support DHCP/DNS
Table:

Modbus addres DEYE= 1;port 502
ADDRESSREGISTER MEANINGUNITDESCRIPTION
598U GRID L1VNapetost omrežja faza 1
599U GRID L2VNapetost omrežja faza 2
600U GRID L3VNapetost omrežja faza 3
604P GRID LD L1WMoč na tokovnem transformatorju v inverterju faza 1
605P GRID LD L2WMoč na tokovnem transformatorju v inverterju faza 2
606P GRID LD L3WMoč na tokovnem transformatorju v inverterju faza 3
607P GRID LD TOTALWSkupna moč s tokovnih transformatorjev v inverterju
616P GRID CT L1WMoč na tokovnem transformatorju zunaj inverterja faza 1
617P GRID CT L2WMoč na tokovnem transformatorju zunaj inverterja faza 2
618P GRID CT L3WMoč na tokovnem transformatorju zunaj inverterja faza 3
619P GRID CT TOTALWSkupna moč s tokovnih transformatorjev zunaj inverterja
627U BACKUP LOAD L1VNapetost iz razsmernika faza 1
628U BACKUP LOAD L2VNapetost iz razsmernika faza 2
629U BACKUP LOAD L3VNapetost iz razsmernika faza 3
651P BACKUP LOAD L1WMoč na razsmerniku faza 1
652P BACKUP LOAD L2WMoč na razsmerniku faza 2
653P BACKUP LOAD L3WMoč na razsmerniku faza 3
212BATT CHARGE LIMIT CURRENTAOmejetev moči polnenja baterije
213BATT DISCHARGE LIMIT CURRENTAOmejetev moči praznenja baterije
214BATT DIS/CHARGE PERCENTAGE%Status napolnjenosti baterije
215U BATTVNapetost baterije
216I BATT (+/-)ATok polnjenja/praznenja baterije
672P PV1 (string 1)WMoč fotovoltaičnih modulov string 1
673P PV2 (string 2)WMoč fotovoltaičnih modulov string 2
676U PV1VNapetost fotovoltaičnih modulov string 1
677I PV1ATok fotovoltaičnih modulov string 1
678U PV2VNapetost fotovoltaičnih modulov string 2
679I PV2ATok fotovoltaičnih modulov string 2

Description is in my language (Slovenian) everything else I write in English.

If someone read's more data please complete table.

This table is for Deye 12K-SG04LP3 (on modbus port pin 7 and 8)

Kind regards. Peter
Hi,
Have you tried the Wifi/RS232 port ?
Where is the modbus port? I manual I can find a port called RS485/CAN is that the one?
Br. Jacob
 