My unit is barely a month in service and appears to be bonding N-G on battery. Purchased through watts247.
Before you return- disconnect incoming/outgoing power. See what N-Gs are on battery only. Mine was closed grid-Green to Inverter-Green, and inverter N-G are closed. No grid connection like I said.
Try it
I have the lv2424 and it definitely does NOT bond N/G on battery....even tho they said it does; probably varies by model and they have only a single answer they give out ;-)
when it comes to bonding you have to deal with a variety of situations:
1)plugged in, on grid: LNG are all present and wired thru
2)plugged in, on battery(when grid line power drops) NG are still present and wired thru, L is coming from AIO not grid; you
may still be getting bonding via input and output N's getting tied together...and the N/G bond in the panel gives you your bonding like always.."maybe"...
3)
UNplugged, on battery; incoming LN are lost, you still have G(if you wired in a separate ground) but its floating from N
in the case of 1&2 you could still have N/G bonding in your panel if the AIO is bonding neutrals only together...
for case 3, if you have lost your neutral pathways and the AIO is ONLY providing N-to-N bonding on battery you will have lost your ground bond.
sady there is no "clean" way to solve this other than adding in your own controlled transfer switch with correct bonding based on your specific AOI wiring... if you have lost the grid input entirely(unplugged) you really need to test your system to see what it is doing. I had an older transformer based inverter that not only switched all 3 wires but had a jumper you could install that would cause another relay to bond G/N on battery. It weighed a LOT and cost a lot hehe...
next is a terrible idea ;-)
a "not recommended but I did it anyway" is to bond the ground and output neutral...this WILL result in "double" bonding (BAD) in your wiring when you are plugged into the house/grid, but does mean you can yank the plug right out of the wall and everything will have a "proper" N/G bonded ground path. If you end up with even slight ground currents this will pop GFI circuits so fair warning.
sure wish there was some type of "standard" for the inverter market but there is not and asking the company rarely gets you an answer from someone that "really" knows what is going on.