When you are combining over 150V, you need the Midnite PV6-250 combiner to hold the higher voltage 300V breakers. He's probably referring to that. https://www.midnitesolar.com/produc...e=Combiners&productCat_ID=9&sortOrder=6&act=p
you are MAXED out of solar charger the rest of your panels are being unused....Here is an updated screenshot from right now. Still cloudy I guess.
Exactly, which is how he currently has it, and we are working out how to change that. We're just figuring out what equipment he has, and what changes are needed.That would put the panels in parallel
Perfect.Here is an updated screenshot from right now. Still cloudy I guess.
I have been hoping for a full sun day but hasn't happen. I am just trying to decide the best route to take so wanted to confirm I understand what the options might be.....
1) Keep the 12V inverter and add another Midnite 250 charge controller. In this case I should get double what I am getting now but will be over-panelled. So approx. 1600 watts?
2) try to exchange for 24V inverter and with current set up (just one Midnite CC) the system will generate approx. 1700-1800 watts as per Hedges?
3) If I went with 24V inverter and another Midnite 250 CC what could I expect for Watts to be generated?? Would this boost it above the 1800 Watts?
A couple of questions. When talking about the size of breakers, do I just look in the combiner box and see what size of breakers are in there? Is it simply stamped on them?
If I did upgrade to 24V inverter, what size would I need in terms of Watts? Still 3000 Watt or smaller/larger?
Thanks everyone for their help and advice.
i would have thought the same. that is a lot of battery reserve.... at least it has shown the other design issues with this systemOk thanks for the info. To be honest just left the inverter on because I didn’t know to turn it off and didn’t realize it would drain the batteries.
How about low battery shutdown? I read spec for his model inverter as saying doesn't shut off until 10.2V.I'll answer the breaker question, I think Ryang did a good job with #3. If you have a Midnite PV3, you most likely have 150V breakers. They look like this. If they gave you 300V breakers, they will be double breakers, and end up looking like 4 breakers in a box designed for 3 breakers, so modification would have had to have been done. The 300V breakers look like this.
If we switch to a 24V system, the Victron BatteryProtect could do the trick. Available with or without Bluetooth. https://www.victronenergy.com/battery_protect/battery-protectHow about low battery shutdown? I read spec for his model inverter as saying doesn't shut off until 10.2V.
Do you have a retrofit shutdown solution? Does Midnight charge controller have a signal which could be used to control inverter or a relay?
Sounds good, except can't support an inverter/charger because only allows current in one direction.If we switch to a 24V system, the Victron BatteryProtect could do the trick. Available with or without Bluetooth. https://www.victronenergy.com/battery_protect/battery-protect