The external CT's are place on the power cables from the utility and have correctly been calculating the Grid power into the inverter and out of the inverter for over a month. As you can see below from the two pictures below that were taken at the same time, the CTs are correctly showing that there is 2907 watts going to the Grid. This agrees on both the graph and the display. The problem is that the consumption is being recorded in the data file and on the graph as 1882 watts when in reality it is only 188 watts as you can see on the display. The display is correct, the graph is 10X higher than it should be.thanks for sharing this here @Dcuste
most likely the CTs have some issue or are clamped in the wrong way.
Where's the CT's arrow toward? the correct way should toward the inverter.
And where you clamped the CTs? let's look into this. Thx
I don't think this problem is because of the CTs at all, but I find it strange that ratio was somehow changed in the settings and a lot of pLoad data was corrupted around the same time.