New Member
How would YOU handle the AC-out wiring for 3+ inverters paralleled in single phase 120v to a breaker panel? The system is fully off grid with N + G bond at the panel and bonding disabled for each inverter.
I'm leaning toward using 2P breakers for each pair of inverters to light up both panel legs, then jumping the legs at the main lugs. All other breakers will be 1P.