Bringing up a generator and dropping the load onto it like it was a UPS can and does create issues. Ideally you want the generator to start with little or no load so that it has a chance reach full rpm and to stabilize. After up and running than loads can be introduced without putting as much stress on the generators ability to maintain voltage and frequency.
I think you said, "I want a Sunny Island."
It starts the generator, gives time for warm-up, synchronizes inverter output to generator, closes relay to parallel.
Current draw from generator is limited to programmed amount, balance from batteries.
After disconnecting from generator, it is allowed a cool-down period with no load before being shut off.
Periodically, generator is started and run to exercise it.
Different battery SoC trigger generator operation during night vs. day, to avoid noise at night if possible.
With suitable generator characteristics of frequency vs. load, AC coupled PV inverters deliver their full output power when needed, curtail production only if load becomes so light that generator spins up to higher RPM. Of course, Sunny Island monitors for backfeed, and disconnects generator as needed to prevent that.
Perhaps some other inverters with off-grid history have similar functions.