Ok heres the deal
Over a year ago I built a huge TEMPORARY 4P4S battery
SHORT STORY
The battery is falling out of balance as we approach 100% SOC... 1 cell block will creep higher than the others (the highest I saw was about just over two tenths of a volt
These cells have been in service for about a year
These will be in this configuration only temporarily eventually they will be reconfigured to 16S but that is probably two or three months away
I am considering tearing this pack down and configuring them at 16p for a top balance... After all it has been over a year since the last top balance
In addition I'm considering adding an active balancer as I have been told that battery management system simply can't handle balancing such large cell blocks. (304 ah ×4 = 1216 ah)
LONG STORY
I used 16, Eve Cells, 304ah from Docan
Initially I did a 16P top balance to 3.65 volts
Are we configured to 4p4s and installed 200 amp battery management system with Bluetooth (JBD?)
I also installed it in parallel with another lifepo4 battery
I had no serious issues out of these cells slide from a very occasional misbalance on cell two... It wasn't a huge difference but it would creep up a little bit relative to the other cells this would all sort itself out after a few charge and discharge cycles
Every now and again the batteries would reach full charge and disconnect charge abruptly. This only happened on days when it was cloudy sometimes but the sun would come out from time to time... It also required that there was little to no load on the battery
What would essentially happen is after the charge disconnect happened It would cause the charge controllers to not react quick enough and feed too much voltage to the inverter causing an inverter shutdown
I solved this issue by lowering the charge controllers maximum charge voltage meaning that the battery would only charge to about 3.45 volts per cell (previously I was using 3.65 volts per cell)
Over a year ago I built a huge TEMPORARY 4P4S battery
SHORT STORY
The battery is falling out of balance as we approach 100% SOC... 1 cell block will creep higher than the others (the highest I saw was about just over two tenths of a volt
These cells have been in service for about a year
These will be in this configuration only temporarily eventually they will be reconfigured to 16S but that is probably two or three months away
I am considering tearing this pack down and configuring them at 16p for a top balance... After all it has been over a year since the last top balance
In addition I'm considering adding an active balancer as I have been told that battery management system simply can't handle balancing such large cell blocks. (304 ah ×4 = 1216 ah)
LONG STORY
I used 16, Eve Cells, 304ah from Docan
Initially I did a 16P top balance to 3.65 volts
Are we configured to 4p4s and installed 200 amp battery management system with Bluetooth (JBD?)
I also installed it in parallel with another lifepo4 battery
I had no serious issues out of these cells slide from a very occasional misbalance on cell two... It wasn't a huge difference but it would creep up a little bit relative to the other cells this would all sort itself out after a few charge and discharge cycles
Every now and again the batteries would reach full charge and disconnect charge abruptly. This only happened on days when it was cloudy sometimes but the sun would come out from time to time... It also required that there was little to no load on the battery
What would essentially happen is after the charge disconnect happened It would cause the charge controllers to not react quick enough and feed too much voltage to the inverter causing an inverter shutdown
I solved this issue by lowering the charge controllers maximum charge voltage meaning that the battery would only charge to about 3.45 volts per cell (previously I was using 3.65 volts per cell)