The electrician told me the split is in the meter box. The 200A single breaker box by the meter was required so that all power going to the house could be shut off by the meter. I updated my first post in this thread to reflect this.Yes. If someone can remove the dead front on the disconnect and the 150 panel, you could see how the 200A panel is fed, and also the wire size feeding everything.
Is the south side of the house the only place for your arrays? How do you plan to get the PV wiring from them to the inverters? Through the house or by trenching around it? Keep in mind that any high voltage PV will need to be in metal conduit once it enters the house.
Edit to add: There doesn’t appear to be any breaker tying the two panels together, which means that the 200A garage panel is fed either from a tap off the 200A main disconnect, or possibly from a feed-through lug on the 150 panel. Either way, it would be good to know the conductor size feeding the garage, and what peak loads that panel supplies.
Consider using the power pro conduit box and the parallel cables per the layout showed in the manual, as you won't need a separate battery combiner for a 4 battery 2 inverter setup, and can have nice clean install.Here are my new plans: Plan Set
Would the breakers in the inverters suffice?Provide 2 additional 200 amp enclosed breakers in the garage for the inverter outputs, to meet nec disconnect requirements per section 705 and 706
Due there being exposed live parts exposed when the door is opened to access the breaker this doesn't meet NEC 2020 705.20(4). In addition there is no means provided to lock the built in breaker in the open position as required by NEC 2020 706.15(A)(3) .Would the breakers in the inverters suffice?
Looks good, I would note where the bond is on the plan.
I have a 400A meter box that will feed the 400A fused disconnect.That 7406 transfer switch is not rated for service entry.
Does your existing 400A main panel have stabs rated to accept 200A branch circuit breakers? If so you might be able to use them to feed the inverters without needing the 200A enclosed breakers.
You can use flexible conduit, but inside the building there some rules in NEC 2202 690.31(D)(1)Does it matter if the steel conduit for PV string wires is flexible?
If you use search on this forum typing "Bluesun", you'll find many Bluesun users including me. I also have two Bluesun (plus two Deye/Sunsynk/Sol-Ark) inverters to go with them. My panels are 700W shingled cell bifacials and I'm pretty happy with them so far. IRC I paid 0,35c/W a year ago including 24% VAT and postage, so they were cheap for me and perfect for my installation setup. Just last Friday I bought 14,3kWp more panels, but this time I don't need bifacials so went with GCL 550W halfcut monofacials as they were just 0,19c/W including everything. Panel prices seem to plummet here when winter/snow comes.@Fearless hi how do you like your Bluesun panels?
I just went live with 50 bifacial Bluesun panels on Thursday.
I was wary because I can’t find a single review or user that has any review of the Bluesun panel. So I’m not sure if they’re outputting what they should or did I just get ripped off on the panels…