Is it recommended to have a disconnect switch, fuse or breaker between the solar panels and the MPPT?
I agree with all the answers, but my question is "why wouldn't you"Is it recommended to have a disconnect switch, fuse or breaker between the solar panels and the MPPT?
No. The less stuff to go wrong the better!Is it recommended to have a disconnect switch, fuse or breaker between the solar panels and the MPPT?
I agree with all the answers, but my question is "why wouldn't you"
I put in a 20A DC circuit breaker which can also be manually tripped (this one) on each of my DC circuits (panel to SCC, SCC to battery). I'm in Australia so I bought that one, but you must be able to find something similar.
View attachment 86735
If 3 strings or more are in parallel. Only needs a disconnect if each string is treated separate. An example, the LV6548 has 2 PV inputs per unit. If there are 2 LV6548's in parallel configuration and there are 4 strings each separate with each string running to one PV input, only a disconnect for each string would be required.Yes
If only 1 or 2 strings, you can just have disconnect.
If 3 or more strings, each string needs to be fused.
I agree.Either way, a maintenance disconnect is suggested.
Yes, 3 or more strings only require fusing if paralleled.If 3 strings or more are in parallel. Only needs a disconnect if each string is treated separate. An example, the LV6548 has 2 PV inputs per unit. If there are 2 LV6548's in parallel configuration and there are 4 strings each separate with each string running to one PV input, only a disconnect for each string would be required.
If 2 strings are put in parallel at the PV array and then split into 2 at the SCC with 2 PV inputs, it would not require a fused disconnect.
I agree.
Should never do this, with mppt charge controllers.If 2 strings are put in parallel at the PV array and then split into 2 at the SCC with 2 PV inputs, it would not require a fused disconnect.
kromc5 has been doing it for some time.........Should never do this, with mppt charge controllers.
They will fight each other for control over the circuit.
It can be done with PWM charge controllers, with some efficiency losses.
It's a free world.kromc5 has been doing it for some time.........
https://diysolarforum.com/threads/v...l-specs-of-the-whole-system.11532/post-396563 Start there, works just fine.It's a free world.
Well, mostly.
I'm guessing that one wins the battle, and the other gets whatever is left.How does a MPPT SCC find the maximum power point on 1/2 of a circuit?. How for that matter does it know to take only half of it?. It just plain doesn't make sense. Each SCC needs it's own dedicated array.